LISTEN PLEASE....
i am not on any code, there are no code requirements there. i don't even have to pull an electrical permit. i just want to be safe and i don't want to waste money for something that doesn't need to be.
this is a new code requirement, obviously things ran fine before they placed this into existance. any one that is an electrician wire detached buildings that way before.
if you could do things any way you wanted I AM SURE that there would be portions of the NEC that you would exclude.
Agreed. It's cheaper to do it right than defend yourself in court, even if you win. Plus, somebody still suffered.If it's your place you can do what you want if it's a customers property and you don't do it to code and god forbid something goes wrong you'll find out that the customers insurance company doesn't go by the "no code" provisions.
Besides,, why do it wrong if you know the right way to do it???
If I am understanding you correctly:
1 the power company does not allow services to be attached to the home.
1 the power company requires disconnect.
2 you are required to install the grounding conductor from the disconnect to the house.
3 you can use triplex from meter to disconnect.
QUESTION doesn't the disconnect have to be located within 30 feet of the house to comply with NEC? if so mount disconnect on a poleas close to the house and run your quadplex froim there (i.e. 150 foor run use triplex for 130 feet set disconnect and run quadplex.
MODERATORS FEEL FREE TO CITE PROPER CODE ARTICLES AS THEY APPLY MY BOOK IS HOME ANDI DON'T HAVE THE ARTICLES MEMORIZED9especially since the rearranged it.
RW, it's the same reason we no longer use 3 wire receptacles for ranges and driers, safety. The forth wire, the grounded wire, give a low impedance path back to the "main" panel or disconnect to operate the OCPD. I'm in N.E. Kansas and know what you're saying about "no code" or needing permits. If it's your place you can do what you want if it's a customers property and you don't do it to code and god forbid something goes wrong you'll find out that the customers insurance company doesn't go by the "no code" provisions.
Besides,, why do it wrong if you know the right way to do it???
wrong or right that is the question......
if you were an electrical contractor and your county hadn't adopted the 2008 code yet what would you do?
I would do it in accordance with the most recent code. Just because you don't need to do it to code, or city x, or county y, or state z hasn't adopted it, unless they have issued something stating that you will not do something specified in that code, why not use the most current information and guidelines that are out there?
The "no code" stuff is exactly why our state has started the CEU's being required to maintain our licenses, hopefully someday they'll start with a state issued license as well. But, that's a topic for another thread.
i mean just look at the new requirement for childproof receptacles....good grief the cost difference between two is large. if the ahj doesn't require it, then ec's more than likely won't put it in UNLESS other ec's are doing it. apples to apples. if you are doing it and they are not you are losing money and will soon be out of business.
Yes and no, the (equipment) grounding conductor IS connected to the grounding elctrode system and it can be connected at multiple points. The grounded conductor is only connected at one point, that is at the service entrance point. Utilities may require two connections, one at their side and the oterh is the NEC required at the service entrance point. (This is really not good, since it reduces the effectiveness of the grounding, but for legal reasons there is no way out of this.)I think I understand.
The grounding conductor (4th wire) serves an entirely different purpose than the grounding electrode system of the ground rods and water main.
If you want to look upon it in terms of a back up, than it would be a backup to the grounded conductor.
The 4th wire IS your ground from the source.
RWreuter,
"""
... insurance adjusters know their is a NEC ...
"""
I see the sequence this way.
* There are 30thousand plus electrically related fires each year.
* NFPA Engineers design rules of safe installation to control fires.
* Local Code Enforcement applies the rules of safe installation.
* Insurance companies calculate their $$$ Insurance Rates
on the basis of these rules being enforced, which reduces fires, which reduces insurance payouts.
* Local homeowners have lower $$$ Insurance Rates because the NEC rules are enforced.
Comments are welcome.
Sorry to hit you with a question to an old post:I also like to understand the "whys" of the code. As best as I can understand, the reason for the change is to try to reduce the amount of current that is flowing through the earth during normal operating conditions.
Current takes all paths available. When you use the grounded conductor (neutral) as the ground (like you are used to doing), current that is on the neutral will have some of the current going back to the source (transformer) through the earth. It's very little when the grounded conductor is in excellent condition. If the grounded conductor should start having some higher resistance developing, the amount of current going through the earth will increase.
I'm of the understanding that there is a push to start isolating the grounded conductor starting at the PoCo transformer (which would require a ground and a grounded conductor from the transformer and the grounded conductor would never be grounded again). The NEC has no jurisdiction over the PoCo.
Like others have said, the NEC normally doesn't just make stuff up to mess with electricians. I understand your frustration (I have it with 310.14(C)). The bottom line, if you want to be one of the best electricians around you need to follow the code in your wiring methods.
Sorry to hit you with a question to an old post:
310.14 (C)?
What year is that from? I don't have that section in the 2008 code.