Sure that was the first measurement
212v on nominal 208v drops to
194v at entrance on inrush
194/208=%/100
= -6.73% typical at Srvc conductors
Poco measured different =)
Very similar #s at elevator room
Still vd could be for the first reason
W soft start configured wrong
Great
Easy fix (by others)
Or
Too small Xfmr. Expensive
Or
$rvc conductors ($mall pipe)
Or
Loose nuts at the origin
Possible but
Only for big 3phase load? Goose chase
212v on nominal 208v drops to
194v at entrance on inrush
194/208=%/100
= -6.73% typical at Srvc conductors
Poco measured different =)
Very similar #s at elevator room
Still vd could be for the first reason
W soft start configured wrong
Great
Easy fix (by others)
Or
Too small Xfmr. Expensive
Or
$rvc conductors ($mall pipe)
Or
Loose nuts at the origin
Possible but
Only for big 3phase load? Goose chase