We are now at 103 posts.
1. There are tenants that see lights flicker when the elevator runs. Do all lights on all circuits always flicker at all times that the elevator starts to move? Do any not flicker, or flicker less? Do the lights sometimes not flicker when the elevator starts? At any other times than when the elevator starts do lights flicker?
THE FLICKER HAPPENS AT THE MAIN.
as far as I know ALL INCANDESCENT LIGHTS FLICKER every time THE ELEVATOR GOES UP.
I have seen the elevator cause the voltage to dip every single time it has gone up.
THE COMMENT ABOUT COUNTERWEIGHT AND MAX LOAD WAS VERY INTERESTING
2. This thread started on the question of whether the power company source was weak. This implies making measurements at the demarcation point between the power company and the customer. From the photographs this appears to be where the meters are located.
We have to assume that the only common impedance between lights and the elevator comes from the power company transformers, and the service lines from the transformers to the distribution area where the meters are located.
THERE IS A SOLAR SYSTEM ATTACHED WITH I PRESUME NET METERING, BUT THIS SHOULD NOT HAVE ANY EFFECT ?
The power company source appears to be a wye from three separate transformers. No way to know how the primaries are wired. Thus, there really are three separate 120 V single phase sources that happen to have a synchronized phase relationship to each other. Also it is reasonable to assume 0 impedance feeding the transformers.
Individual single load tests from a hot line to neutral can give us an estimate of the source impedance of that particular phase. This means measuring the change in voltage and the corresponding change in current from just before the ltest load is applied to just after, then Zsource is approximately Vchange/Ichange. The absolute voltage is not of concern, and therefore neither is the minimum voltage. One can estimate the line and transformer impedances, add them, and then compare the calculaed source impedance with the measured source (internal) impedance.
The source impedances for the three phases should be moderately close together.
I CAN DO MORE DELTA V WITH P-N 40A LOAD
Load tests begins typically with 6a per leg and then I toggle in a 40a P-N load instantaneously
https://1drv.ms/i/s!AkuU8mYuf3eEgVbEZrpB0QU9AQRz
Measured VDelta WAS 2.2; 2.14; 1.25 - so one leg was about half the change of the others!
CAN REPEAT THE MEASUREMENTS WITH EXTRA ACCURACY TO CONFIRM
3. Three 120 V light bulbs were connected from the three phases to neutral at the main panel. What was visually observed when the elevator started? Did all three flicker at the same time? Was the amount of flicker the same for each bulb? Was the amount of flicker the same for every elevator start? Do tenants see more or less flicker at their location, than at the main panel? Is flicker extremely quick, 100 mS, or longer, 500 mS?
FLICKERED ALL AT THE SAME TIME
INTENSITY VARIES: I SAW "A" LEG AS GETTING DIMMER, COLLEAGUE SAW THEM AS SIMILAR
REMOTE LOCATION UNK- PRESUME WORSE BECAUSE OF FEEDER DROP
I can go up to the furthest unit to measure minimum or delta V if needed.
Not a short FLICKER, MORE LIKE 500MS
4. When using min-max measurements in this type of test the measurement needs to be started just before the load change occurs, and ended just after the load change. So RESET just before load change, then immeadiately after the load change readout min and max.
Can information and values from yesterday for these various points be provided?
WE DID THREE TESTS PER PHASE WITH THE MINI LOAD BANK
MIN MAX
CRUDE LOG HERE
https://1drv.ms/i/s!AkuU8mYuf3eEgVbEZrpB0QU9AQRz
3LIGHT TESTS VIDEOS HERE
https://1drv.ms/f/s!AkuU8mYuf3eEgVqZj62jhqPsrp74
but only the 500ms duration is really clear.
The lights dip pretty good.
P-N voltage at the remote elevator disco was down to 104V