"usually it just runs over temp."the stated facts
no over temp
Why do you continue to refute that?
"usually it just runs over temp."the stated facts
no over temp
"usually it just runs over temp."
Why do you continue to refute that?
1000 kVA.I'd like to see how a utility would size their transformer to feed that load
Good. We seem to be finding some common ground.1000 kVA.
Good. We seem to be finding some common ground.
You seem to miss the point of this thread. See post# 126.
The evidence is clear cut. The transformer goes overtemp.
Perhaps you missed the smiley? No problem.I guess I'm glad someone thinks that's funny. I sure don't.
Um, I wasn't aware of any political comment.Perhaps you missed the smiley? No problem.
Anyway, the transformer is simply not big enough regardless of how Ing wants to manipulate his digits
Perhaps you missed the smiley? No problem.
Anyway, the transformer is simply not big enough regardless of how Ing wants to manipulate his digits
On one side ingeniur statement that transformer KVA is adequate and there is no clear cut evidence on OP side it is not so. On the other side, American Electrician Handbook states KVA be equal to hp. What issue arises if the latter is not complied in OP case?
1000 kVA.
not according to the opThe evidence is clear cut. The transformer goes overtemp.
OK just to chuck another pebble in to pool. UK DNO’s (PoCo’s) rate their transformers for cyclic overload at 125% summer, 150% winter.
Following a transformer failure we ran its partner at 120% continuous for 3 months. It was a 2nd hand unit of venerable age acquired from a military base so solidly built. All we did was add a couple of fans blowing over the cooling radiators.
Yes according to the OP.not according to the op
Yes according to the OP.
Why do you continue to dispute this fact?