In general, when would one use a zig zag instead of a delta-wye?
Maybe, just maybe, you meant to say "wye-delta" grounding transformer?
I dont believe so.....If I wanted to make a grounded system out of an ungrounded system, I could use a 1:1 voltage ratio transformer with the ungrounded supply connect to the delta primary and the ground the wye secondary, no? I assume the reason to use a zig zag would be it is an autotransformer so it could be smaller and cheaper, however not sure how real world economics like common availability come into play...
If a ground is desired on a delta system to allow for line to ground faults to trip a breaker, zig zag can be used.
If the only reason is to provide a grounded system at a secondary, then the delta-wye works, but line ground primary faults do not trip.
If you say why not just use a wye to wye transformer, now the harmonics all go to the neutral causing a plethora of other problems (white wire turns brown, :weeping:etc). Remember, in a delta-wye, the triplett harmonics are all in phase in the primary thus are short circuited - which brings up the point that the delta windings need to be heavier copper to carry the short circuited harmonics. That impacts the economics of the overall situation also.
Interestingly, the only zig zag xfmrs I've ever seen actually installed at a service drop were at Minuteman LCFs. Had never heard of them prior to that (1970).
Why not just use a wye delta and connect your ungrounded system only to the wye primary.
There's a world of difference between the Zig-Zag vs Delta-Wye used as a derived-grounding source for an ungrounded system. And, frankly, I always chose the former!
Using a delta-> wye only gets me that latter and I need a relatively large transformer. What is the comparison between the zig zag and using a wye->delta as an autotransformer?
The other use is as the secondary for a variant on the delta-wye isolation transformer that shifts the phase relationship between primary and secondary. This can be used for harmonic mitigation.
how much is the phase shift? Clearly a delta-wye already shifts 30 degrees....