1793
Senior Member
- Location
- Louisville, Kentucky
- Occupation
- Inspector
M. D. said:It does not say directly above the bathtub area or decking ,...it says what it says ,"directly over a bathtub"
What happend to Charlie's rule ??
Point taken!
M. D. said:It does not say directly above the bathtub area or decking ,...it says what it says ,"directly over a bathtub"
What happend to Charlie's rule ??
mthead said:.....2002nec-406.8[C]Bathtub and shower space.
A recptacle shall not be installed within a bathtub or shower space.
2002nec410.4[D]bathtub and shower areas=3'horizontally from waters edge;8'vertical from waters surface.
While the naysayers will argue that 410.4 applies specifically to luminaires an inspector will calmly explain that " the bathtub area/zone referenced in 406.8" is only defined in 410.4.
Panel Statement:Section 406.8(C) is intended to be different from 410.4(D).
Cord-connected and similar luminaries are required to be grounded and are not
required to be protected by GFCIs. They are, however, prohibited from being
installed near or above a tub or shower zone. Receptacles, on the other hand,
are required to be both grounded and protected by a GFCI. Further, they are
required to be installed at the sink location. In many bathrooms, it is impossible
to install a receptacle if it is also prohibited from being installed within 3 feet
horizontally of a shower or tub.
lpelectric said:And I would thank you for your cooperation and readily sign off once you moved it to the front as permitted in 210.52(D) Exception. :smile:
M. D. said:I wonder what "suggestions" he would give if a wall light were installed in a shower stall subject to shower spay and everything
electricmanscott said:Yeah, good luck with that. It ain't happening, sign off or get the hell out and send in an inspector that knows what they are doing.
This is not that difficult folks. (well for most of us anyway) First grade reading level.
No receptacles directly over a bathtub. That receptacle is not. Have a nice day.
iwire said:????
Your building offical can change the rules at will?
Thats sucks for ECs.
wbalsam1 said:This remark appears to me to be downright nasty and mean spirited. At the least very sourcastic.
Ipelectric said:I can help the installer and the homeowner consider what's necessary for safety.
wbalsam1 said:Ouch! Remind me not to get on your bad side.....
M. D. said:
How far away from this baby David
inspector 102 said:I am not sure whether it has been mentioned yet, but the International Residential Code has requirements for clearance between the tub unit and a lavatory. The 4" clearance is intended to allow enogh space between fixtures to allow proper cleaning. If there had been a space provided between these fixtures, I do not think the receptacle placement would have even been an issue.
lpelectric said:In an effort to start the day out right, I yield to electricmanscott & M.D. who have convinced me of the error(s) of my ways.
The "doublespeak" was caused from changing my mind due to post # 44 from iwire. This made sense.
Those posters that helped me to remember that the code is what it is, not what I think it is, I note special attention to and thank you for your helpful reminders.
lpelectric said:Where is this in the IRC? :smile: I've been unable to find it.
Kontrols said:As long as the recepticle is GFCI and conveineint to the sink (which it is) I see no issues. In fact it is required not only as a bathroom recepticle but also under NEC 680.71 to be within 5' of the tub.
Kontrols said:As long as it is a GFCI I see no problem. In fact, because it is a Jacuzzi tub it must be within 5' of the inside of the tub (NEC 2005 680.72) and it appears to meet the requirement for the bathroom sink also.
The only remaining issues is whether it is conveinent for its purpose and whether "one" plug can meet the bathroom GFCI and Hydromassage GFCI and I think so although there are some inspectors who are not so flexible.
dnem said:All it says is that any plug within 6' of the tub must be GFCI protected.
David