Mr. McDowell,
Thanks for the update on the device version of the AFCI. Too bad it is not yet available (as far as we know). As I am in an area covered by the 2005 NEC, an AFCI device would permit me to provide AFCI protection to all but the first six feet of the branch circuit emanating from a legacy panel unsupported by the Big Four manufacturer's limited AFCI breaker models.
Minuteman,
While I understand that you could think that GFI protection at just one receptacle is not like AFCI branch circuit protection to just one outlet, I have to agree with Mr. McDowell that the example given by Jeff Sargeant of the NFPA in Post #46 is a good comparison.
I read the point of the NFPA statement as being: A new outlet in a bedroom (an outlet extended off an existing circuit) must have AFCI protection, as a new outlet in a bath must have GFCI protection.
Thanks for the update on the device version of the AFCI. Too bad it is not yet available (as far as we know). As I am in an area covered by the 2005 NEC, an AFCI device would permit me to provide AFCI protection to all but the first six feet of the branch circuit emanating from a legacy panel unsupported by the Big Four manufacturer's limited AFCI breaker models.
Minuteman,
While I understand that you could think that GFI protection at just one receptacle is not like AFCI branch circuit protection to just one outlet, I have to agree with Mr. McDowell that the example given by Jeff Sargeant of the NFPA in Post #46 is a good comparison.
The existing outlets are not required to be afci protected when an extention of the circuit is added to connect to a new outlet, however, in order to provide AFCI protection to the new outlet extended off an existing circuit, the only available AFCI equipment must be in the form of a breaker, and, therefor, the remainder of the branch circuit, in addition to extension to the new outlet, will receive AFCI protection.mcdowellb said:I called the NFPA last month to ask them this example: If I add a receptacle to an existing circuit in the bedroom and their response was yes, that new outlet would have to be afci protected, not every other outlet. He also said that it was no different than adding an outlet in the bathroom, the new bathroom outlet would be required to be gfci protected.
I read the point of the NFPA statement as being: A new outlet in a bedroom (an outlet extended off an existing circuit) must have AFCI protection, as a new outlet in a bath must have GFCI protection.