I did an inspection of a 1 family dwelling a while back and found these items:
- Kitchen lighting on with small appliance bc
- Flexible cord used for every circulator at the boiler rather than a permanent wiring method
- Csst not bonded to the GES (plumber's responsibility)
- Duplex receptacle used for the clothes washing machine in the basement on concrete floor. (either use a single receptacle, or gfci protect the duplex)
- Same as above for sump pump
- Only 1 outside gfci protected receptacle for the whole house