Joe Rocker
Member
Quick question, how many #14 THHN solid or stranded wire can be pulled through half inch emt? How many #12?
Thank you
Joe
Thank you
Joe
Quick question, how many #14 THHN solid or stranded wire can be pulled through half inch emt? How many #12?
Thank you
Joe
Quick question, how many #14 THHN solid or stranded wire can be pulled through half inch emt? How many #12?
Thank you
Joe
I'm assuming that Joe doesn't have a codebook handy.
#14=12
#12=9
Quick question, how many #14 THHN solid or stranded wire can be pulled through half inch emt? How many #12?
Thank you
Joe
Is it a nipple? Can you use 53% fill?
so I can put 12 or 9 respectivly in EMT. so is a nuetral current carring and can I add a isolated ground wit each of thoughs circuits..so would it 4 circuits with a ground or circuits wit 6 isolated grounds..or just a flat 9 or twelve wires regardless of current carrying conductors..
Yup.It's a raceway fill question. Nothing more.