MazzEE
Member
- Location
- Atlanta, GA US
I have a room 11'-9" x 23'-9", (279 sq ft).
Based on 210.71(B)(2) NEC 2017, "A meeting room that is at least 12' wide and that has floor area of at least 215 sq. ft. shall have at least one receptacle outlet located in the floor at a distance not less than 6' from any fixed wall for each 215 sq. ft. or major portion of floor space."
Based on my example with one dimension less than 12', and one greater than 12', it is physically impossible to be greater than 6' from any fixed wall.
Therefore i do not meet the requirements of this part of the code and no floor outlets are required. Is my understanding correct or do I need the two floor outlets as shown?
Based on 210.71(B)(2) NEC 2017, "A meeting room that is at least 12' wide and that has floor area of at least 215 sq. ft. shall have at least one receptacle outlet located in the floor at a distance not less than 6' from any fixed wall for each 215 sq. ft. or major portion of floor space."
Based on my example with one dimension less than 12', and one greater than 12', it is physically impossible to be greater than 6' from any fixed wall.
Therefore i do not meet the requirements of this part of the code and no floor outlets are required. Is my understanding correct or do I need the two floor outlets as shown?