Oh, c'mon now!!!
Couldn't they afford a real Scotsman?
Perhaps one actually with the WattsPower factor VA, and Watts.
Hope this helps.
Why? You missing some?Do you have any grey poop on?
But of course.Do you have any grey poop on?
The order in which you learn them doesn't change what actually happens.
Real power is never negative. Negative power means power is flowing back to the source. Can't be real power if it is returning to the source from the load.Don't think that's correct.
For the period where the voltage is positive and the current is negative, the first 30deg for example, the real power is negative. The same applies to those periods where the voltage is negative and the current is positive.
Your chart shows real power (in green) as always positive.
Reactive power on the other hand is both positive and negative, and averages out to zero. Its positve power is stored energy which is then returned to the source in the negative half-cycle of its waveform.
Apparent power (the green line on your graph, magenta on mine) is also positive and negative. Its average is the same as real power. FWIW, instantaneous power represents apparent power.
After scrutinizing my graph more carefully, it was not correct (don't know what I was thinking :rollDon't think that's correct...
In the instantaneous domain, yes."Apparently", apparent power = real power + reactive power.
This one any better ??? ...
Um.....Real power is never negative. Negative power means power is flowing back to the source. Can't be real power if it is returning to the source from the load.
I said real power. A capacitor (not accounting for losses?an ideal capacitor) uses no real power. Pavg is zero.Um.....
Take a power factor correction capacitor.
It consumes no power (other than losses).
It does have an applied voltage and it does take current.
Their product, times sqrt(3) if it is three phase, gives you VA, or apparent power. It is also entirely reactive - after all that's why you use PFC.
So we have reactive VA and zero W.
If the power can only be positive, as you are suggesting then, it would have to be zero all the time.
This just proves my point. The [ideal] capacitor uses apparent power, no real power.But that's not what happens. Over the first quarter of a cycle the capacitor charges to a positive voltage. It takes energy (0.5CV^2 Joules) from the supply over that period. Energy is power times time thus the supply has to provide power. During the next quarter of a cycle the capacitor discharges to zero volts and thus zero energy. Power goes back into the supply. Negative power.
Here it is for one cycle.
Sure I can... and I did. While I agree they are based on RMS values, those would be of voltage and current rms values. What we are after is Pavg.One other comment. Real, apparent, and reactive powers are based on RMS values. You cannot display them on a waveform diagram that shows instantaneous values.
In the instantaneous domain, they have to be.Interesting. So real, apparent, and reactive power are all in phase agreement, right?
I was showing the RMS domain on an instantaneous graph (which is what I was thinking, for which I later said I don't know what I was thinking :rollIn your previous graph, real power was shown in phase (though double the frequency) with voltage and reactive power likewise with current.
Yes, we associate the power with the value of Pavg... But does it not stand to reason if we use Pavg, apparent, real, or reactive, then there is a waveform associated with it?I agree. The real power is the average value of the instantaneous power. Note that for the pure capacitor, the average, or real, power is zero.