This is the UL Guide for "Engine Generators for Portable Use" FTCN.
It prohibits the use of an interlock kit as the transfer equipment, but only if you are using a listed engine generator. 110.3(B) would trigger this requirement for listed generators, but there is nothing in the NEC that would require the transfer equipment to switch the grounded conductor when using a non-listed portable generator to power a building.
FTCN
This is the UL Guide for "Engine Generators for Portable Use" FTCN.
It prohibits the use of an interlock kit as the transfer equipment, but only if you are using a listed engine generator. 110.3(B) would trigger this requirement for listed generators, but there is nothing in the NEC that would require the transfer equipment to switch the grounded conductor when using a non-listed portable generator to power a building.
GENERALThis category covers internal-combustion-engine-driven generators rated 15 kW or less, 250 V or less, which are provided only with receptacle outlets for the ac output circuits. The generators may incorporate alternating- or direct-current generator sections for supplying energy to battery-charging circuits.
When a portable generator is used to supply a building or structure wiring system:1. The generator is considered a separately derived system in accordance with ANSI/NFPA 70, "National Electrical Code" (NEC).2. The generator is intended to be connected through permanently installed Listed transfer equipment that switches all conductors other than the equipment grounding conductor.3. The frame of a Listed generator is connected to the equipment-grounding conductor and the grounded (neutral) conductor of the generator. When properly connected to a premises or structure wiring system, the portable generator will be connected to the premises or structure grounding electrode for its ground reference.4. Portable generators used other than to power building or structure wiring systems are intended to be connected to ground if required by the NEC.