Assuming a single 400 amp OCPD It is not even enough for 400 amps if it was just 10' away.
Not even close. CU, yes.
It's closer than I thought once I looked it up in the table for dwelling units. hmy:
Unless he has more than one main.
Two 200 amp main breaker panels with a total calculated load under 350 and he is good to go.
Correction... In pa they call it 400 amp, but its only 320amp
My on concern was voltage drop... At what distance to you have increase conductor size?
Again it depends on the load. If you want to use the 400 amp load then you will have to calculate it but you are ignoring some info the others are giving you.My on concern was voltage drop... At what distance to you have increase conductor size?
A 400 amp meter base is rated 400 amps for non continuous loads but only 320 for continuous loads. A 200 amp meter base is rated the same way. 200 amps for noncontinuous loads but 160 for continuous loads.
My on concern was voltage drop... At what distance to you have increase conductor size?
If the calcuated load is 399 amps can I use the 400 amps meter base?
Yes you can as the NEC calculated load has already accounted for the continuous and non-continuous loads.
Picture a standard 400 amp panel, in truth it is also rated 320 continuous 400 non-continuous.