400 amp feed thru panel:

xt3sty6Nc9vaG4fW1Cg7PJt3bJEZy2xlP2fvryNsvtg=w691-h921-no
So being an inspector and also not knowing when this was installed, as nice as this is, you could be getting a correction notice from me.
 
Every time I think about unloading my tools and doing some highly professional work at home I end up with my wifes tools and an un workman like outcome.

Sent from my SPH-D710BST using Tapatalk
 
A guess: 2005 NEC, so 210.4(D) {2008} is not applicable.
Is there even any MWBC's installed in that photo? Looks like there are a lot of neutral conductors for all the circuits to be MWBC anyway, maybe there is one or two MWBC's. And there isn't even enough visible in the left panel to make any comment on this as being a possible issue.

I think 2014 NEC wants to somehow ID which neutral goes with which ungrounded(s) even if just a two wire circuit - can't check at the moment, but can someone verify that?
 
210.4(D) oh and I did say "could".


As stated under the 2005 not applicable. With a new code change under the 2014 this would be code compliant without grouping the MWBC's since each conductor is individually numbered. :cool:
 