sparkyrick
- Appleton, Wi
Personally I haven't seen an EGC on a toaster. My toaster is pretty old though.
OK, I probably picked the wrong item for that scenario, LOL!
However for large appliances like a range, fridge or dishwasher I dont see that taking place. About the only real risk is installer error not hooking up the EGC which would be a code violation to begin with.
About that plugged in and bonded toaster-someone will have the metallic utensil in one hand while trying to hold down ( and touch the now bonded metal shell) the toaster with the other-thats the hazard and a good reason for not bonding that casing.
I think that the assured egc option on those outdoor job sites has more to do with risk- you will be wearing work boots and you generally wont be grounded that well- an egc will not protect you if you come into contact with current while you are grounded. Walking through a puddle of water on the ground outdoors that has a damaged cord draped thru it is a far cry from being standing bare foot in energized water or on conductive damp surface while touching a bonded frame (a direct connection back to the source) of an appliance.
Installer Error..... Probably not as unlikely as you would like to think.
In a new house or business an electrician may be involved with the installation of appliances but what happens when they are replaced?
In many motels and apartments the maintenance personnel replace appliances and many are not all that qualified. In homes either the owner or a person working for the seller replaces appliances. We would like to think these are qualified technicians but I wouldn't count on it.
If you work in people's homes you will find lots of missing grounds as the houses get older. May be just a loose connection or where someone that didn't know what they were doing tampered with the circuit. It happens
the assure grounding program basically says the real risk is an open EGC. On large appliances the is not likely.
Which is cheaper, to install a GFCI protected receptacle with a test button or have someone come out and test the circuit on a regular basis.
How far should code go to protect DIY screw ups?
Which a change or at least a clarification of intent was needed - disposers was one item that raised questions immediately when 2014 come out and whether or not their "receptacle" where cord and plug connected was considered to be within six feet of the sink.NEC 2014
210.8(A)
(7) Sinks — where receptacles are installed within 1.8 m
(6 ft) of the outside edge of the sink
Currently added in the 2017 ROP:
For the purposes of this section, when determining distance from receptacles the distance shall be measured as the shortest path the cord of an appliance connected to the receptacle would follow without piercing a floor, wall, ceiling, or fixed barrier, or passing through a door, doorway, or window.
Sink may be grounded by other means - maybe there is a disposer in there that introduces a grounded object.That is true and very likely in small portable appliances both from plugging & un-plugging along with the cord becoming damaged, but such is not common for large appliances.
I agree, however in the US most toasters are two prong so if the plumbing is plastic the GFCI would in theory hold.
We are installing and being inspected to the '14
AFCI branch , GFCI as required.
New appliances all have NRTL sticker, major American manufacturer
Appliances will not tolerate '14 requirements
Manufacturer 'tech support' openly advocating code violations
Can't close this job out .....Can't get paid.......Can't make everyone happy
Who's authority do i hail to?
~RJ~
But sometimes they still trip due to inductive kickback, popular name brands are more resistant but not totally immune to tripping from inductive kickback.GFCIs look for imbalance, if none is flowing then it will not trip them.
Kind of answered what I was going to say to what I quoted from you above --- many of these code changes in more recent years put the contractor on the hook for a lot of design issues that should be put on some manufacturers. We have to install per code, but reality is what is code puts a lot of inconvenience to users - and they demand the contractors to fix those problems, contractor goes to manufacturer of products involved and gets nowhere when it comes to a solution that will meet codes and make user happy. If something is actually broken or defective that is one thing, but we have products out there that are required to be used and others that don't play well with the required products. And stuff that is changing so fast - things you sold only 5 years ago are now obsolete and you can't find parts or support for them.True
Nobody wants to make the call, and the EC takes the fall.....
~RJ~
You keep saying this like you know this to be a fact.
It is not a fact, it is simply your guess.
I'll simply say this - if we had a body or injury count from electrocution and shock from large residential appliances, then we would have GFCI rules for them long before the current 2014 rule existed.
Most anything with electronics anymore has MOV's that shunt surge current to ground. I seldom see GFCI issues with them though. Problem is everyone cries about how much a freezer of warm food costs because GFCI opened the circuit. It still cost a lot less then a loss of life because the appliance had a ground fault and the EGC failed to facilitate OCPD operation, and one can buy monitors or alarms to tell them their freezer is not working if they want. I will admit I find this to be a bigger issue in garages and unfinished basements but may come up more in kitchens with this six foot rule from the sink. I also think I see more missing EGC pins in garages and unfinished basements on such freezers or refrigerators then I typically find in the kitchen - probably because the kitchen does have an outlet in a space that is dedicated for a refrigerator. Garages and basements you are more likely to find extension cords used to connect these appliances.I know that. It can be grounded several ways. But thats not what I am saying. My point is immersion alone is not a concern. If it was everything would have ILCIs.
Which if true is the reason why GFCIs should not be on refrigerators. One thing common to most Fridges is that leakage current is naturally higher due to the large amount of internal wiring, most of which rest against grounded metal. The distributed capacitance is higher then say a toaster oven. Second the electronic control boards have MOVs that shunt to ground.
How likely the above is to trip a GFCI I can only guess on this one, but some people do make a good argument regarding with the above.
That aside it peanuts compared to the inverter compressors pulling power through AFCIs.
I agree - other then the mentioned garages, unfinished basements, etc. this is not normally much of a problem. And even in those areas maybe not too much of a problem with appliances themselves, but like I said above - that is where you see extension cords being used and then the potential for trouble does increase. In particular extensions that are missing an EGC, or only using a two wire extension and removing the EGC pin from the appliance cord.I'll simply say this - if we had a body or injury count from electrocution and shock from large residential appliances, then we would have GFCI rules for them long before the current 2014 rule existed.
I agree. Second I looked at the ROPs, the evidence used to support it was incredibly thin imo.
I am curious.
When these ROPs were submitted, did you submit a comment opposing them?
Have you submitted any new proposals for them to be deleted or amended?
Dennis Alwon said:That would be true with a two wire connection but it would trip the gfci with a toaster that has an equipment grounding conductor. You must think of all scenarios not just one case where it may not trip.mbrooke said:Im betting the GFCI doesn't trip either if the plumbing is plastic.
Dennis Alwon's statement was false. While hand-held GFCI testers fail to trip GFCI's, without a grounding conductor to shunt test current, the GFCI device itself only monitors (Hot, Neutral) for imbalance. GFCI's are designed to ignore grounding wires, for use in accordance with 406.4(D)(2), in homes built without grounding wires.No matter what I do not see a kitchen fridge likely to end up without an EGC. I will agree people cut off the ground pin for extension cords, but not in kitchens.
Dennis's information was wrong, and inadvertently perpetuated your confusion between 2 or 3-wire connections. You may have been Punked or punked perhaps the subject of forum entertainment, by those that enjoy burning grasshoppers more than answering their questions.