Another C10
Electrical Contractor 1987 - present
- Southern Cal
- Electrician NEC 2020
Ok, maybe a little vague .. Hint : only some times the tenant would get a jolt when turning on the switch to the bathroom light.Anyone care to guess what issue occurred when this bath switch was used after taking showers. I removed the cover and saw this.
yes, you win a cigar .. So I approach this switch and flip it on, no stray voltage, I remove this cover to find waded tissue paper in there as seen, I remove the device and come to find the tissue is cool and barley moist, I figured there it is, now thinking ok the moist paper is allowing a voltage to pass from the un protected termination screws to the metal of the device, then it dawned on me the reason more than likely this problem was periodic was when someone was in the shower, the walls would get moist, no exhaust fan .. therefore moisture could drip down between the wall plate and then leach onto this tissue paper.Ungrounded device strap, damp paper, metal plate screws . . .
so what would you think by looking at this image caused the blue flame. and how.
Sorry .. ok Yes the sheathing allowed for the exposure of the element no one can determine, although after I mention it you probably will see it.Hard to play this game when there's such little information provided, and the goal posts keep moving.
I was gonna say that next.Rat urine, . . .