WasGSOHM
 - Montgomery County MD
 - EE
In a symptom-free house and most stuff off, I measured 5A in the half inch diameter aluminum service neutral
and noise (means less than 10 mA) in the 20' of a 1/8" diameter conductor that runs to the panel bus and to the inlet cold water pipe clamp.
There is another conductor to earth ground at the power pole 30' away.
The equivalent circuit so far is a ground current source (not a voltage source) through a ground resistance through the service neutral to the panel ground bus out the 1/8" diameter wire to the water pipe and back into the ground.
The other loop that touches the panel ground bus is the capacitively coupled current from all the hot wires to all the ground wires.
With 15 breakers and 100' of Romex per breaker and 100 picofarads per foot for Romex, I get a capacitive reactance of 1/(377 x 1.5E-7) and is 18kohms of reactance. At 120 v this is about 7 mA and this agrees with the less than 10 from above but I have to think about the 5A.
More to come. . .
More to come. . .