mbrooke
Batteries Included
- United States
- Technician
Then write one and submit a PI to the appropriate technical committee.
Closing me eyes- "no supporting evidence, reject"
Exactly. You have to have actual incidents that caused a problem to make a change like that.Closing me eyes- "no supporting evidence, reject"
Do you have specific incidents in mind where a code change would have made a difference? Without a history of a problem codes are not changed.I know.
The question is how many more incidents do we need?
Why do people have to learn about these things on the news or in court rooms?
That is because there was a TIA that removed health care occupancies from that list. Healthcare is not under the purview of NFPA 70, it is an NFPA 99 issue. The tie between NFPA 99 and NFPA 70 is article 517. The fact that health care requirements were in Article 700 was that CMP overstepping their role.
If 99 wants those requirements in 517 they will be put in 517. They have the purview over the rules.But what if NFPA 99 wants 700 requirments for the life safety branch? Or did so at one point?
We have 517 for two reasons...99 is not often legally adopted, but 70 is. The second reason is that the rules in 99 are more performance based and those in 70 are more prescriptive.And there in lays the issue, the heart of all tragedy.
So why even have 517?
You think Texas isn't wishing for a time machine?
I have no idea...have never studied 99.So why is NFPA 99 ok with generator and fire protection on the life safety branch but nothing for the critical branch?
However, a lot of the rules are based on cost. Hospital administrators have a seat at the table in the 99 technical committees. That is one of the major reasons 517 has coordination, and 700 and 701 have selective coordination.
Have a good night, I am done with this70s rules appear stricter than 99.
I still can't figure out who exactly put life support on the back burner to the point it was eliminated.
This borders, if not flat out stemming on...
which maybe wouldn't be so bad, if we made up the dif in 'isolate in place' building codes elsewhere....~S~Very sad to see the code eliminated what was present US hospitals and what is still required for hospitals in all other developed countries
Shelter in place is the only option, the power system must reflect this.
in a broader overview.....along with every other system MBrooke ~RJ~