oldsparky52
- Wilmington, NC USA
I didn't see where the cabling was identified as BX, but that would fit with everything else I've read here. I agree that there is a high resistance connection of a conductor to the BX on circuit #10. Since the voltage at the receptacle is reported as in post #47, I think the connection is between the neutral and the sheath.Sounds as if the customer not really interested in finding and fixing the why. I think Brant said it had BX wiring. Most times I've seen based on reported age of installation, a bonding of neutrals from multiple circuits was done. I've seen those numbers many times from just that situation and some were in a hidden jbox, covered by sheetrock or a cabinet installed over it.
Another scenario BX sheath can act as grounding conductor in limited fashion and if there is a high impedance connection connection between the conductors and the sheath maybe from nail or screw, the ground of the appliance can become energized. Given voltage readings present when connecting between washers enclosure to unrelated grounded circuit seems would be very likely. And without a ground connection back to the breaker it would never trip. Pulled one out once that had a finish nail driven dead center through the hot conductor of a NM wire, been that way for years (best guess based on customers statement). Literally a hole in the center of the copper of a #12 wire. If that been a BX the sheath would have become energized and without an adequate connection for grounding would never trip breaker.
Appears the washer is on a grounded receptacle with no grounding conductor back to source. If receptacle is bonded to box that has the above situation then it will carry into any grounded appliance plugged into it. One thing I haven't seen mentioned is if a test to meter between the receptacle box of #10 circuit and the dryer enclosure for voltage. Another confirmation not commented on is if an ohm reading between the N/G on appliance plug was done to determine if there was a high impedance N/G leakage inside appliance.
A lot of good ideas posted. I particularly like Larry's suggestion about connecting a jumper from the washer to the dryer frames and put an amp meter on it.
IMO this is one of those problems that it's cheaper to abandon that circuit, but what to do about the lights.
I feel for Brant, I never liked being in the position he is in.
Brant, did you ever test the conductors with an ohm meter when you had them disconnected (I didn't think you had your megger with you)?