kwired
Electron manager
- Location
- NE Nebraska
Someone already mentioned it, but if it is a newer unit with variable speed drive that likely is a contributing factor, though I can't put that in with the fact he only seems to have a problem when connected to breaker position #10.
Run a temp circuit with intact EGC (even connected to breaker 10) and I'd guess your frame voltage goes away. But if you also GFCI protect it, it very likely trips the GFCI because there is leakage current.
Run a temp circuit with intact EGC (even connected to breaker 10) and I'd guess your frame voltage goes away. But if you also GFCI protect it, it very likely trips the GFCI because there is leakage current.