If there's a bootleg ground, then this part of the OP implies there is definitely a neutral problem, as two points on the neutral wiring should not have (so much) voltage relative to them: "Washing machine has 37v on the frame when measured to any neutral or frame of adjacent dryer."It could be a bootleg ground on the receptacle (I hadn't considered that in my previous post)
But if the washer and freezer receptacles don't have bootleg grounds, I'm liking a partial hot-ground fault in the washer ground "island". Which won't trip any breakers as the circuit has no EGC.
For testing purposes, one could plug the washer into one of the circuit 10 receptacles with a 3 to 2 prong "cheater" to see if disconnecting the EGC in the cord affects the voltage measurement. If it doesn't, how is either the cord hot or cord neutral getting connected to the washer case? That shouldn't happen, and the problem should be present on any receptacle, which it is not.
Cheers, Wayne