ptonsparky
Tom
- EC - retired
What are the receptacle devices? Two wire?
Do they share a noodle Brant?I moved #10 breaker to #12 space to see if the condition existed on both legs of the transformer, and it did.
~RJ~
Did you try unplugging the dryer and checking the voltage? I may have missed something about where all you were checking for voltage to frame or neutral. I say there is a neutral problem somewhere.
well, seems you're dealing with a 'return path' ...jmho BrantTurned off every circuit breaker except #10; problem still existed
h*ll, it could be a bum noodle next door , and municipal H2O Old one.....Well running an equipotential bonding conductor between the machines and water piping should mitigate the symptoms of the problem, but the problem would still exist.
It almost has to be the neutral conductor between the panel and light box, ... right?
If that home-run bypass used same breaker, whats best way to check breaker(s) for high resistance?The eyebrow raising thing for me is that it only happens on circuit #10
Looking for voltage between points that should be at the same potential.If that home-run bypass used same breaker, whats best way to check breaker(s) for high resistance?
I used an extension cord to plug the washer into various other receptacles, and it only happens while plugged into the conductors of Circuit #10.
Does not fix the problem. Just hides itI'm still thinking what I suggested in post #2. Create an equipotential bond.