dwils1980
- Fort Collins Colorado
- Master Electrician, Building Inspector
With that said does one trump the other?One could have evaluated the combination being used together but the other did not.
Ok, first off this is NOT going to apply to any panel listed after 1995, which is when UL changed the rules. That change meant that breakers are either “Specified” or “Classified”. Specified means that the PANEL MANUFACTURER has specified certain breakers from another manufacturer to be tested and listed for use in that panel. Since 1995 that is usually only their own, breakers but the exceptions are the smaller panel manufacturers such as Midwest who don’t make breakers.Should this be going both ways though? If the panel lists different breakers as acceptable but the different breaker manufacturer either doesn't carry a Classified listing or it does but does not list said panelboard as an approved part of their Classified listing?
Eaton, & Siemens, both make a UL classified replacement for some SQ D QO panels.I know at one time you could buy a classified breaker made by GE that fits Square D QO panels, probably even had one that fits Eaton's CH panels. Those make some sense, as those two product lines are different enough that nothing else physically fits them anyway. I don't know why one would bother to get a classified breaker to fit the somewhat universal design that is used by most 1 inch wide (single pole space) breakers out there, other than for some replacement in something that has been discontinued. Chances are the classified breaker will cost you more than the one made by the OEM.
I figured that is likely. Around here a genuine QO breaker is pretty readily available and probably cost less than purchasing any classified breaker to fit a QO panel. The GE version is just one I remember seeing in some local hardware store a long time ago. I don't know why they even had it as they also sold genuine QO breakers.Eaton, & Siemens, both make a UL classified replacement for some SQ D QO panels.
I see no reason to use them either, if my memory serves me, they were only for single phase panels and not for use in series rated systems.I figured that is likely. Around here a genuine QO breaker is pretty readily available and probably cost less than purchasing any classified breaker to fit a QO panel. The GE version is just one I remember seeing in some local hardware store a long time ago. I don't know why they even had it as they also sold genuine QO breakers.
If I am not mistaken Siemens QP are also Listed for MP-T or whatever Murray was but not the other way around.Siemens never did it for their QPs, although they were already interchangeable with most Murray panels (not Arrow Hart / Murray or pre Crouse-Hinds / Murray) because when Siemens bought Murray from Crouse-Hinds, they switched to using the QP breakers in Murray panels with just changing the stickers (and UL files).
Actually Connecticut Electric got a license from Siemens to test QP breakers in a bunch of panels including BR and sells a standard QP breaker as a 'classified' breaker. So you can use a QP breaker in a BR panel. You can find them in big box home improvement stores.Connecticut Electric did it with a few legacy lines, that’s it.
I just had a circumstance with an old Murray panel. Had to upgrade poll motor to gfci protection. The only siemens DP gfci breaker available was/is QPF. I tried VERY hard to install the siemens breaker. just would NOT install on the back "hooks"(where breaker hooks onto to opposite the bus bar). I reached out to Eaton to see if they manufactured a CL double pole GFCI breaker. The only manufacture BR gfci breakers. The best O could do was a BR style. The BR fit. looks to me it was that or nothing. Try telling a homeowner that they need to swap out a panel to install a breaker....I see wrong breakers in panels all the time. (Homeline, too.) It doesn't seem to lead to problems, but in my opinion it's a sing of hack work.
Plug on neutral breakers are not physically interchangeable.
Are you saying any QP, or one with a CL label?So you can use a QP breaker in a BR panel.
sorry about attachments. are bryant still manufactured? do they manufacture a gfci breaker?Your attachments are both the same.
If the Murray panel is old enough to SAY on its label that you can use the Bryant breakers, that’s fine.
There was no extra label or stamp on those "Connecticut Electric" Siemens QP breakers, just a Siemens QP breaker in a plastic package.Are you saying any QP, or one with a CL label?
Bryant, no. BR, yes; by Eaton.sorry about attachments. are bryant still manufactured? do they manufacture a gfci breaker?
That sounds about right. The Siemens breaker wouldn't go at all. But the BR would go just fine.Wait, wait....... Did the OP say new breaker in older Murray panel ????
If i read that right, i know why the breaker wont seat. Some (maybe all?) of the pan rails had 2 small rejection pieces under the "hook". These are designed to be removed with a special tool which I have never seen. They can be removed safely with a long nose plier AFTER turning off power to the panel.
I have had to do this, it isnt difficult, just needs care in doing it
Hope this helps.
Howard
I have never seen that. And I've seen plenty of old Murray panels. Curious. Anybody got a pic?Wait, wait....... Did the OP say new breaker in older Murray panel ????
Hope this helps.
Howard
I think Siemens modified there’s to fit Homeline too now. At first, nobody’s fit Homeline.I remember some the marketing hype when Homeline first came out was interchangeability. They claimed they would plug into nearly all others with similar design but the others would not plug directly into a Homeline panel.
I've seen more Homelines plugged into other panels than I have seen others plugged into Homeline panels. Not sure if others changed to fit Homeline or if that was just rumor from the start of Homeline existence. I never really tried to plug others into Homeline myself so not really sure.
Maybe that wasn't official hype from Square D but rather from the distributor(s)?
Then there is Milbank, Midwest and a few others with pedestals, meter mains, etc. that list multiple breaker manufacturer lines as acceptable to plug into their equipment.
There is this FAQ from SQ D's parent company, https://www.se.com/us/en/faqs/FA129931/I think Siemens modified there’s to fit Homeline too now. At first, nobody’s fit Homeline.
Gosh so if I just read the breaker types on the panel label and replace with a breaker that says it's that type on the breaker, then basically I'm good.Here's an on topic Eaton memo, to add to the mud.
With all this confusion, anyone up for a return to Type S fuses?