 - Licensed Electrician
The metal to metal contact from all the parts does all the bonding. If the standard lock ring was any kind of special bonding connection there wouldn't be any reason for bond bushings or bonding lock rings.
			OK... in this case, with a chase nipple, use a bonding lock ring inside the second box and land a ground wire on it from the first box, which we will assume is bonded by way of an EMT coupling and regular locking ring. This way the second box is also bonded.The metal to metal contact from all the parts does all the bonding. If the standard lock ring was any kind of special bonding connection there wouldn't be any reason for bond bushings or bonding lock rings.
Yes, the metal to metal contact does the bonding. To me the chase nipple itself does not bond anything. It does not have a threaded nor bolted connection to the butted box that it is inserted from. (Sorry if this is worded awkwardly)The metal to metal contact from all the parts does all the bonding. If the standard lock ring was any kind of special bonding connection there wouldn't be any reason for bond bushings or bonding lock rings.
That's not necessary since everything involved is already metal.OK... in this case, with a chase nipple, use a bonding lock ring inside the second box and land a ground wire on it from the first box, which we will assume is bonded by way of an EMT coupling and regular locking ring. This way the second box is also bonded.
No, it's not worded awkwardly. The lock ring on any fitting isn't the sole bonding connection. The metal fitting, (in this case a chase nipple, but it could be a seal tite connector, emt connector, threadless rigid connector, etc) the metal enclosure, the metal lock ring all work together to bond all the parts. You don't ever need two lock rings or extra wire in this context. You don't even need two lock rings with threaded rigid conduit, you can use a lock ring on the back and a metal bushing on the end of the conduit.Yes, the metal to metal contact does the bonding. To me the chase nipple itself does not bond anything. It does not have a threaded nor bolted connection to the butted box that it is inserted from. (Sorry if this is worded awkwardly)
But what documentation have you seen that says it CAN be used to bond two objects together?A chase nipple is designed to connect two metal objects together. I've never seen any documentation that suggests it cannot be used to bond those two objects together.
Doesn't the lock-nut accomplish that with any connector?I don't see the removal of paint being described when using a chase nipple and locknut to bond two enclosures together. But then I am imagining painted enclosures.
Sure, against the surface it digs into, but when there is two boxes butted against each other, no.Doesn't the lock-nut accomplish that with any connector?
I have pondered that. I don't think a chase nipple is long enough, but a star washer might work....
As I said earlier, would adding a second lock-nut work on the flange end?
Have used that method but nothing beats a copper ground wire.The proper way is to use a close nipple or other suitable length nipple, four locknuts and two bushings.
Now everybody's happy.
-Hal
EXCEPT ARGENTI !!!Have used that method but nothing beats a copper ground wire.
It's latin for silver like what the periodic table symbol is based on.
Yeah I was thinking the same thing. Are there any specific application guidelines in the instructions or listing? I don't really like two enclosures butting together.Question, having trouble picturing. Two enclosure and connecting via a chase nipple, the space between the 2 enclosures would be inadequate to put the covers on? Chase nipples don't leave any space between the 2 surfaces.
AFA acting to serve as bonding connection between the 2 enclosures don't see the issue so long you make a clean bond, no paint. Other option would be to add bonding bushing to the chase nipple and wire bond thru to the flanged side of nipple's enclosure.