There needs to be something in place to protect us from conflicting requirements.
Sure, but you were responding to a question about using a receptacle.Tesla's instructions here are specific to the hardwired unit.
For a hardwired unit, you'd still need to GFCI protect it if it is outdoors at a dwelling unit and on a 50A circuit or smaller per 210.8(F). But indoors, or on a 60A circuit, you wouldn't have to.
Cheers, Wayne
210.8(F) is new for 2020, not sure if it changed in 2023.Isn’t that new for 2023?
Cheers, Wayne
I've been spying on the forum for well over a decade, but I just signed up a few minutes ago. The Tesla 60a chargers have a Maximum of 48 amps output. 48x1.25=60a but the load is 48 amps, so I think the next size up rule would apply. Also, I've ran a Neutral in the past for plug in chargers because it just seemed weird to install a receptacle and leave a terminal empty.