- New Jersey
- Journeyman Electrician (retired)
I'm curious what everyone is using when an emergency disconnect is required for a one family dwelling. I see that for less than $200 a 200 amp Square D QO outdoor circuit breaker and enclosure can be purchased instead of a non-fuses disconnect. Can this be used as the EM disconnect keeping the service disconnect as the main in the panel located inside? IMO it complies with 230.85(3).
230.85 Emergency Disconnects.
For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit current rating equal to or greater than the available fault current, installed in a readily
accessible outdoor location. If more than one disconnect is provided, they shall be grouped. Each disconnect shall be one of the following:
(1) Service disconnects marked as follows:
EMERGENCY DISCONNECT,
SERVICE DISCONNECT
(2) Meter disconnects installed per 230.82(3) and marked as follows:
METER DISCONNECT,
NOT SERVICE EQUIPMENT
(3) Other listed disconnect switches or circuit breakers on the supply side of each service disconnect that are suitable for use as service equipment and marked as follows:
Markings shall comply with 110.21(B).