 - Wisconsin
 - PE (Retired) - Power Systems
This is so far off.Yes, but the latter case won't give you 100A in the primary. You only get 100A through the primary if you have 100A through all of the secondary pieces.
The amp-turns on the primary and the secondary are equal. So if, say, the full primary and secondary are 10 turns, and we have 100 amps through, say, 3 turns on the secondary, and 0 amps through the other 7 turns on the secondary,
Assume you have a transformer with 100A flowing through a 4 turn primary, on the secondary there are also 4 turns so there would be a corresponding 100A. This works out to be 25A per turn of flux.
Now take that same transformer secondary and cut it into two pieces/windings of 2 turns each, with no other changes passing 100A across 4 windings with 25A per turn of flux will result in 100A across the 4 turns of the primary.
Now with a center tap between the two secondary windings. Have 100A flow through one winding and 0A flow through the other. This results in 50A per turn, which is 2X the original amount of flux
This gives us the same flux density as the original condition so we would get the same 100A across the 4 turns on the primary.