mhosier
- Manteca, Ca
210.52 (C) (2) (a) now requires "At least one receptacle outlet shall be provided for the first (9 ft2), or fraction thereof, of the countertop or work surface. A receptacle outlet shall be provided for every additional (18 ft2), or fraction thereof, of the countertop or work surface."
The question has come up is a duplex receptacle considered two outlets? Example: Island with a square foot measurement of 30 ft2, if they have a (2) gang box with (2) duplex receptacles, does that cover the intent?
The definition of receptacle states "multiple receptacle is two or more contact devices on the same yolk..."