hillbilly1
- North Georgia mountains
- Owner/electrical contractor
Are the lugs in the ATS rated for two wires?
Hmm, yeah you can. Flat sealing washer. $3?You can't enter that ATS above the live parts without something like a Meyers hub.
Notice I said "like". Meaning something to seal it.You can't enter that ATS above the live parts without something like a Meyers hub.
Good call!! Appreciate that! Luckily the inspector overlooked it.. but there was no way I was gonna get 4/0-4/0-1/0-1/0 through 160' of 2" with multiple bends.. maybe I can be meet exception no 2 with it being existing conduits that were installed 2 years ago when they planned don having it a 200a service..I'll count my blessings and take this as a learning experience.Oops, you are not allowed to parallel conductors smaller than 1/0.
Thanks for the information..I used what you recommendedThe connection between the connector and the enclosure is not without a sealing washer. At least one manufacturer of PVC male adapters has a sealing washer for there connectors that will give it the required rating to be installed above the live parts.
If the breaker is rated for two wires per lug, or has double lugs, provided you don’t exceed the tap rule length, and yes, the panel would need a main not to exceed the wire rating.Did not know you could take (2)200 amp sets of conductors off of a 400 amp breaker to two different panels. I thought you would have to tap off of them in a wireway/jb and run the 200a rated set to each panel and each panel would have to have a main.
He said it was 160'.If the breaker is rated for two wires per lug, or has double lugs, provided you don’t exceed the tap rule length, and yes, the panel would need a main not to exceed the wire rating.
That’s a good question, is he saying the generator is 160’ away? Or the entire service and transferswitch is 160’ away from the house? After looking at the panel picture, the feed is not back to back, and appears to go across the ceiling, so there is pretty much no way it would meet the tap rule even if the t’switch was just outside the house.He said it was 160'.
What exception 2 are your referencing.Good call!! Appreciate that! Luckily the inspector overlooked it.. but there was no way I was gonna get 4/0-4/0-1/0-1/0 through 160' of 2" with multiple bends.. maybe I can be meet exception no 2 with it being existing conduits that were installed 2 years ago when they planned don having it a 200a service..I'll count my blessings and take this as a learning experience.
Sent from my Pixel 7 using Tapatalk
Thanks for the information..I used what you recommended![]()
Yeah, he has one under there, it is blue, so it doesn’t show up well against the gray.What’s in your picture is a bushing. It’s for wire protection, which, incidentally, I don’t usually use on PVC conduit.
The sealing washer Don is talking about is the (usually) yellow washer, like what is on a LFNC connector.
You beat me to it!the sealing washer is there its blue and built into the lock nut
If the conductors are #4 or larger, the bushing is required, PVC or not.What’s in your picture is a bushing. It’s for wire protection, which, incidentally, I don’t usually use on PVC conduit.
Shouldn't the washer be on the outside?Yeah, he has one under there, it is blue, so it doesn’t show up well against the gray.
I would put them in anyway but if an EMT conductor with the insulated throats do they need bushing?If the conductors are #4 or larger, the bushing is required, PVC or not.
I've always thought so, to seal between two flat surfaces, the connector and the enclosure.Shouldn't the washer be on the outside?