480v high leg motor issue
It is a delta-delta transformer and has no center tap according to posted nameplate. there are voltage adjustment taps on the high voltage side. If OP is having low voltage issues the tap being used could possibly come into play. Being reverse fed situation he probably should use one of the mid range taps though.
It is tapped to #4 468v...getting 472v on the meter
I dont believe it does. So if no winding is bonded to ground, in theory what should my voltages be to ground on the 480 side?
When troubleshooting it is best to make, and provide, all of the possible voltage measurements.
L1-L2
L2-L3
L3-L1
L1-N
L2-N
L3-N
L1-G
L2-G
L3-G
N-G
I know its not referencing a center tap, but what is the dotted line coming off of H1 and X1 referencing?
As Kwired mentioned above... it's a phasing symbol, which shows the phase shift (if any) between the primary and secondary windings.
In a typical delta to wye it shows the 30 degree shift inherent in that type of transformer.
In your delta to delta, it indicates there is no phase shift.
Is this transformer designed for reverse feed of step up?
It appears to be step down.
Notice the label only says HV and LV. If reference feed was prohibited it would use terms like primary and secondary. Sorgel always had application notes on backfeeding their transformers.
My guess is the transformer is almost 50 years old.