480v high leg motor issue

It is a delta-delta transformer and has no center tap according to posted nameplate. there are voltage adjustment taps on the high voltage side. If OP is having low voltage issues the tap being used could possibly come into play. Being reverse fed situation he probably should use one of the mid range taps though.
It is tapped to #4 468v...getting 472v on the meter
 
I know its not referencing a center tap, but what is the dotted line coming off of H1 and X1 referencing?

As Kwired mentioned above... it's a phasing symbol, which shows the phase shift (if any) between the primary and secondary windings.

In a typical delta to wye it shows the 30 degree shift inherent in that type of transformer.

In your delta to delta, it indicates there is no phase shift.
 
Is this transformer designed for reverse feed of step up?
It appears to be step down.
Notice the label only says HV and LV. If reference feed was prohibited it would use terms like primary and secondary. Sorgel always had application notes on backfeeding their transformers.

My guess is the transformer is almost 50 years old.
 
I'm trying to understand it...wouldn't the secondary induced voltage have the same effect as the primary? Wouldnt my voltage on the 480 side be (L1-G 240, L2-G 416, L3-G240)?

Nope. The voltage to ground relation of the primary does nothing to the secondary. Since you have a secondary that doesn't have a center point tap, your choices are to corner ground the secondary or leave it ungrounded.
 
When troubleshooting it is best to make, and provide, all of the possible voltage measurements.
L1-L2
L2-L3
L3-L1
L1-N
L2-N
L3-N
L1-G
L2-G
L3-G
N-G

Notice the label only says HV and LV. If reference feed was prohibited it would use terms like primary and secondary. Sorgel always had application notes on backfeeding their transformers.

My guess is the transformer is almost 50 years old.
Interesting, thank you for the explanation
 
As Kwired mentioned above... it's a phasing symbol, which shows the phase shift (if any) between the primary and secondary windings.

In a typical delta to wye it shows the 30 degree shift inherent in that type of transformer.

In your delta to delta, it indicates there is no phase shift.
Nobody could ever tell me what they were, thank you
 
It’s a step up transformer. Service coming in is 240v three phase high leg. Steps it up to feed the motor.

Just to clarify on the step-up/step-down thing: this transformer was pretty clearly originally designed as a 'step-down' transformer. As others have noted, this transformer is capable of being used as a 'step-up' transformer, and may even have proper documents for such 'reverse' use.

The clue is the location of the voltage adjustment taps. The voltage adjustment taps change the 'turns ratio' between primary and secondary, so that you can get the correct secondary voltage even if the primary voltage is a bit out of spec.

In the vast majority of cases the voltage adjustment taps are placed on the primary side of the transformer. This lets the voltage adjustment change both the turns ratio of the transformer and adjust the magnetic flux level in the transformer core. If you place the voltage adjustment taps on the secondary side, then if your primary voltage is higher than nominal the transformer core will have excessive saturation and losses.

I have a drive isolation transformer with voltage taps on the secondary side, but this is very rare.

So when you look at that transformer dataplate, and you see the taps on the HV side, you can be quite certain that you have a 480V:240V step down transformer used in reverse.

-Jonathan
 
Just to clarify on the step-up/step-down thing: this transformer was pretty clearly originally designed as a 'step-down' transformer. As others have noted, this transformer is capable of being used as a 'step-up' transformer, and may even have proper documents for such 'reverse' use.

The clue is the location of the voltage adjustment taps. The voltage adjustment taps change the 'turns ratio' between primary and secondary, so that you can get the correct secondary voltage even if the primary voltage is a bit out of spec.

In the vast majority of cases the voltage adjustment taps are placed on the primary side of the transformer. This lets the voltage adjustment change both the turns ratio of the transformer and adjust the magnetic flux level in the transformer core. If you place the voltage adjustment taps on the secondary side, then if your primary voltage is higher than nominal the transformer core will have excessive saturation and losses.

I have a drive isolation transformer with voltage taps on the secondary side, but this is very rare.

So when you look at that transformer dataplate, and you see the taps on the HV side, you can be quite certain that you have a 480V:240V step down transformer used in reverse.

-Jonathan
Interesting, makes sense.
 
Why the change?

Although this isn’t helping the OP.
Not every transformer should be run backwards. As previously mentioned taps are an issue. Some small transformers, like machine tool units less than 3kVA may actually have compensating windings on their primary to account for losses in thier cheaper core construction. Finally there is the probability the increased inrush/energizing current may require primary side OCPD which exceeds the NEC limits.

[Soapbox]
The reality is the NEC has their restriction, for manufacturer approval, because too many installers do not follow manufacturers instructions, especially when they are not included with the equipment. This is similar to how SCCR requirements have been added to article 240, in addition to the historical ones in 110.9 and 110.10, or the specific prohibition of 2 grounded conductors I a termination that accepts 2 grounding conductors.[/soapbox]
 