14gage wire for light switch?

Status
Not open for further replies.

robert pitre

Member
Location
Houma,la
I notice that electrician has been using 14gage wire from light switch ,to lights , and the power come from a 20amp breaker that feeds a room . Is this aloud? Does anyone know were this is at in NEC code book. What about 3 way light switches that uses 14-3 and Gets it power off 20amp that feeds living room? Can it be that the lights want exceed more than 15 amps! :happysad:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
What he is doing is for some reason thought to be acceptable by many but, it is not, read 210.19.

Roger
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
No it is not allowed. The switches and switch legs are part of the branch circuit and should be size appropriately. If they use a 15 samp breaker then it would be compoliant
 

user 100

Senior Member
Location
texas
I have seen this one quite a bit in some older homes where devices were fed through the ceiling boxes( have never liked this method)-they would go 12 for the recs, but would pigtail out to a stretch of 14 for the sw leg-all while on a 20amp ocpd. I don't think it was legal then and I know it isn't today-210.19 does apply.
 
Last edited:

templdl

Senior Member
Location
Wisconsin
I think the electricians justify it as being a tap rule. The caviat is that a lignt s not a correctly sized OCPD as required by the 10 or 25' tap rule.
Their interpretation is definitely a code violation.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I think the electricians justify it as being a tap rule. The caviat is that a lignt s not a correctly sized OCPD as required by the 10 or 25' tap rule.
Their interpretation is definitely a code violation.
If they have any justification at all, it is by analogy to the situation for motors, but the difference is that there the motor overload does provide recognized overload protection for the wire.
And so their analogy fails. :(
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
Doesnt anything say that 120 volt power circuits in a dwelling must be 14 gauge and larger? At least I thought I saw it somewhere but could be wrong.

Table 310.106(A) shows the minimum of #14 copper however section 240.4(D)(1) allows smaller conductors. But I don't know if we can use #18 or #16 as branch circuit conductors.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
According to 240.4 (d)(1 & 2) we can use #18 & 16 as long as we meet their conditions. HMMMM interesting.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Table 310.106(A) shows the minimum of #14 copper however section 240.4(D)(1) allows smaller conductors. But I don't know if we can use #18 or #16 as branch circuit conductors.

My take is you can not, but there could be a loophole Im unaware of.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Table 310.106(A) shows the minimum of #14 copper however section 240.4(D)(1) allows smaller conductors. But I don't know if we can use #18 or #16 as branch circuit conductors.
You can't use them as branch circuit conductors, but you can tap fixture wire in those sizes to the branch circuit conductors to feed a fixture. 240.5(B)(2)
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
The OP stated that the #14 extended from the wall switch to the ceiling fixture. Clearly, this fact renders the argument moot as the length almost certainly exceeds the limitations of the tap rule. Also, overrating NM cable is just bad in any case, whether or not it could be interpreted to be allowed by code. I would not do it. However, the actual ampacity of #14 cable is 20amps ;-)
 

Electric-Light

Senior Member
Example: Two LED ballasts located within the same luminaire can use 18 AWG within it, but interconnecting wires between lumunaires can not be less than the ampacity of the branch.


There are UL listed lamp sockets with a receptacle or a socket to lamp bushing that legally allows something to be plugged into a light socket. A 14 AWG wire to the light switch can allow a 1,500W space heater plugged into a socket holding a 300W light bulb continuously.
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
Example: Two LED ballasts located within the same luminaire can use 18 AWG within it, but interconnecting wires between lumunaires can not be less than the ampacity of the branch.

Well, the fixture has been approved by Underwriter's Laboratories ;-) Your branch wiring has not! :lol:
 