Charlie this seems to support your viewpoint:
(the parts crossed out in the ROP I shrank and italicized, since the cross-out did not copy over.)
2-201 Log #2222 NEC-P02 Final Action: Reject
(210.52(B)(1))
____________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Recommendation: Revise as follows:
(B) Small Appliances.
(1) Receptacle outlets served in the kitchen, pantry, breakfast room, dining
room, or similar area of a dwelling unit, the two or more 20-ampere smallappliance
branch circuits required by 210.11(C)(1) shall serve all wall and floor
receptacle outlets covered by 210.52(A) , all countertop outlets covered by
210.52(C) , and receptacle outlets for refrigeration equipment.
Substantiation: Under the 2005 code wording, if receptacles in addition to
those that are required by 210.52(A) or (C), these additional receptacles are not
required to be supplied by the two or more 20 ampere small appliance branch
circuits. This proposed change will require all installed receptacles in these
areas to be supplied by the small appliance branch circuits.
Panel Meeting Action: Reject
Panel Statement: The panel added the references to make it clear as to what
receptacles had to be on the small appliance branch circuit. The use of the term
?covered? in the text was very specifically chosen instead of ?required? to
avoid the exact issue raised by the submitter.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
____________________________________________________________