Arcingwild
Member
- Location
- Benicia, CA. Us
So it's really not as dumb as it sounds. The panel is a square D sc2040m125pf. The sticker says Bussing is rated 225a max. Mains 125a max. And meter socket 125a max. The insulator behind the meter jaws says 200amp cont.... this panel is being installed as a "like for like" in my house that has a 125a panel currently. POCO said as long as the sticker says 125a max it is considered like for like. I guess my question is couldn't I install this panel now and when I'm ready for the service upgrade to 200a, install the underground raceway get the inspections and just swap the main to 200? BTW, Pocono already approved the like for like after seeing the sticker.