Pinzgauer

Member
Location
Greenwich, CT
Hi everyone –
(To pre-empt some expected responses …. Yes, I will talk to the local electrical inspector but wanted some feedback before I do.)

I am a builder having a friendly disagreement about code interpretation regarding receptacle locations. Talking about the 6’ distance compliance.
The enclosed picture shows a built in bench with drawers, recessed into a wall. My specification called for the receptacle location above the seat as shown in the picture. The electrician, on his own, moved it into the baseboard claiming code requirement.

2014 Code Language:

210.52(A)(2) Wall Space. As used in this section, a wall space shall include the following:
(1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways and similar openings, fireplaces, and fixed cabinets
(2) The space occupied by fixed panels in exterior walls, excluding sliding panels
(3) The space afforded by fixed room dividers, such as freestanding bar-type counters or railings

I have two observations:
1. Since the bench is a “fixed cabinet” (it even has storage drawers) it brakes the wall space and is excluded from the receptacle location requirement.
2. Forgetting my argument above and assuming that it should be included by code, there is no reference in the code as to the height of the receptacles. Therefore, there is no reason why the outlet couldn’t have been located above the bench as specified by the owner and me and still comply with the 6’ distance requirement. The height in itself wouldn’t make it non-compliant.
I welcome your comments.

code.jpg
 

Attachments

  • code.jpg
    code.jpg
    126.6 KB · Views: 2
The cabinet has a wall above it that is within the height required for receptacles therefore IMO you need a receptacle either in the toe space or above the cabinet
 
The cabinet has a wall above it that is within the height required for receptacles therefore IMO you need a receptacle either in the toe space or above the cabinet

Dennis i believe your comment was directed to the two choices presented by the OP.

If the cabinet the built in is less than 12 ft. the required receptacles could be placed as an option to the left and right of the built in shown in the picture.

No matter if a rec. was in the baseboard space or one to the left or right in the dry wall, their is nothing prohibiting a placement of a receptacle in the desired wall space as shown in the picture.

i agree with Dennis a rec. place in the desired wall space could have satisfied the wall space placement required by the NEC.

If the rec. is already cut into the base board as shown in the picture and it is OK with the home owner to leave it, there would be no reason one could not be cut in where the owner desires a rec.

If the owner wants the base board replaced and the receptacle at the desired location, maybe still possible depending on basement, or opening the wall board and doing the repair.
 
To me the wall space is broken by the fixed cabinet so the height of the cabinet is irrelevant. The measurement begins at each edge of the cabinet and the space occupied by the cabinet is not part of the wall space just like the other things on the list, doorway, fireplace, etc.
 
2. Forgetting my argument above and assuming that it should be included by code, there is no reference in the code as to the height of the receptacles.

]

that is not exactly correct

210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. The receptacles required by this section shall be in addition to any receptacle that is:

(4) Located more than 1.7 m (51/2 ft) above the floor
 
To me the wall space is broken by the fixed cabinet so the height of the cabinet is irrelevant. The measurement begins at each edge of the cabinet and the space occupied by the cabinet is not part of the wall space just like the other things on the list, doorway, fireplace, etc.

i would except that argument, there is however wall space within the 5 1/2 feet that is not covered by the cabinet.
some would except that the wall space not being covered by the cabinet should be included in the wall space measurement.

i am under the 2008 code, i see in the section provided by the op it says wall space broken on the floor line
 
Last edited:
i would except that argument, there is however wall space within the 5 1/2 feet that is not covered by the cabinet.
some would except that the wall space not being covered by the cabinet should be included in the wall space measurement.

i am under the 2008 code, i see in the section provided by the op it says wall space broken on the floor line

Fixed cabinets was added in the 2011 NEC.

The exceptions for not being part of the wall space are as follows (numbers added by me):

1) doorways and similar openings
2) fireplaces
3) fixed cabinets

There is no height minimum associated with anything on the list. Any of those items that break the wall space are exempt from the 6'/12' rule. If a fireplace were 4' high would that require a receptacle above it? The answer is no, same applies to a fixed cabinet.
 
Fixed cabinets was added in the 2011 NEC.

The exceptions for not being part of the wall space are as follows (numbers added by me):

1) doorways and similar openings
2) fireplaces
3) fixed cabinets

There is no height minimum associated with anything on the list. Any of those items that break the wall space are exempt from the 6'/12' rule. If a fireplace were 4' high would that require a receptacle above it? The answer is no, same applies to a fixed cabinet.

i agree with the language fixed cabinets broken along the floor line, just wasn't in the 2008
 
Fixed cabinets was added in the 2011 NEC.

The exceptions for not being part of the wall space are as follows (numbers added by me):

1) doorways and similar openings
2) fireplaces
3) fixed cabinets

There is no height minimum associated with anything on the list. Any of those items that break the wall space are exempt from the 6'/12' rule. If a fireplace were 4' high would that require a receptacle above it? The answer is no, same applies to a fixed cabinet.

So actually there should have been a rec to the left and right of the cabinet no greater than six feet from the ends of the cabinet.

The electrician likely took a measurement off the rec. he placed in the baseboard.

I would still allow a 12 ft. measurement from that rec. since it is installed even if the next rec measured more than six ft from the end of the cabinet.
 
So actually there should have been a rec to the left and right of the cabinet no greater than six feet from the ends of the cabinet.

I agree measuring 6' from each of the cabinets edges is what's required. I can see the thinking about the space above the cabinet being wall space but that is no different than the wall space above a door or fireplace, in all of those cases it does not count.
 
I can see the thinking about the space above the cabinet being wall space but that is no different than the wall space above a door or fireplace, in all of those cases it does not count.
I agree. I can't look at the older code versions right now, but my opinion (based on 2017) is that the "thing that looks a lot like a wall" that is above this cabinet is not "wall space," in the context of 210.52. Therefore, no receptacle is required at all. That said, a receptacle placed in either location in the photo would be allowed by code.

By the way, I am about to face a similar question. We are planning a kitchen and dining room remodel for later this year. At the present dining room wall, there will be a built-in banquette that will cover the wall space, left to right, and floor to about 30" above the floor. It will block the existing locations of two receptacles. My opinion is that I don't have to add receptacles for that wall. I might anyway, but code will not require it. That will be a conversation that I will have with the GC and perhaps his selected electrician as well.

 
Any space 600 mm (2 ft) or more in width (including
space measured around corners) and unbroken along the
floor line by doorways and similar openings, fireplaces,
and fixed cabinets that do not have countertops or similar
work surfaces

Would this be a similar space? 2017 IMO, could be argued for the outlet above the counter
 
Would this be a similar space? 2017 IMO, could be argued for the outlet above the counter
I think not. It does not say "similar space." It says "similar work surfaces." We are dealing with a seating area, not a work surface. Nobody is going to need to plug in a toaster or a drill, while seating on this bench. Putting a receptacle is not a bad idea, and not a code violation. But I say it is not a code requirement.

 
I think not. It does not say "similar space." It says "similar work surfaces." We are dealing with a seating area, not a work surface. Nobody is going to need to plug in a toaster or a drill, while seating on this bench. Putting a receptacle is not a bad idea, and not a code violation. But I say it is not a code requirement.


Yep.
 
Thanks for all the replies... Am I correct then when I say that most of you believe there's no requirement for a receptacle within the cabinet space as long as there's receptacles within 6' to the left and right of it.
Thanks again...
 
Thanks for all the replies... Am I correct then when I say that most of you believe there's no requirement for a receptacle within the cabinet space as long as there's receptacles within 6' to the left and right of it.
Thanks again...

Yes. :cool:
 
A generator transfer switch.

Also to respond to some remarks.... yes there are receptacles to the left and right within 6' of the ends of the cabinet.

Okay, in that case you were correct about the cabinet receptacle placement and have the needed receptacles for the wall space; however, you have just failed on working space for that cabinet.

IMO, a generator transfer switch would apply to the following:

110.26 Spaces About Electrical Equipment. Access and working space shall be provided and maintained about all electrical equipment to permit ready and safe operation and maintenance of such equipment.

(A) Working Space. Working space for equipment operat- ing at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of 110.26(A)(1), (A)(2), and (A)(3) or as required or permitted elsewhere in this Code.
 