(To pre-empt some expected responses …. Yes, I will talk to the local electrical inspector but wanted some feedback before I do.)
I am a builder having a friendly disagreement about code interpretation regarding receptacle locations. Talking about the 6’ distance compliance.
The enclosed picture shows a built in bench with drawers, recessed into a wall. My specification called for the receptacle location above the seat as shown in the picture. The electrician, on his own, moved it into the baseboard claiming code requirement.
2014 Code Language:
210.52(A)(2) Wall Space. As used in this section, a wall space shall include the following:
(1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways and similar openings, fireplaces, and fixed cabinets
(2) The space occupied by fixed panels in exterior walls, excluding sliding panels
(3) The space afforded by fixed room dividers, such as freestanding bar-type counters or railings
I have two observations:
1. Since the bench is a “fixed cabinet” (it even has storage drawers) it brakes the wall space and is excluded from the receptacle location requirement.
2. Forgetting my argument above and assuming that it should be included by code, there is no reference in the code as to the height of the receptacles. Therefore, there is no reason why the outlet couldn’t have been located above the bench as specified by the owner and me and still comply with the 6’ distance requirement. The height in itself wouldn’t make it non-compliant.
I welcome your comments.
(To pre-empt some expected responses …. Yes, I will talk to the local electrical inspector but wanted some feedback before I do.)
I am a builder having a friendly disagreement about code interpretation regarding receptacle locations. Talking about the 6’ distance compliance.
The enclosed picture shows a built in bench with drawers, recessed into a wall. My specification called for the receptacle location above the seat as shown in the picture. The electrician, on his own, moved it into the baseboard claiming code requirement.
2014 Code Language:
210.52(A)(2) Wall Space. As used in this section, a wall space shall include the following:
(1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways and similar openings, fireplaces, and fixed cabinets
(2) The space occupied by fixed panels in exterior walls, excluding sliding panels
(3) The space afforded by fixed room dividers, such as freestanding bar-type counters or railings
I have two observations:
1. Since the bench is a “fixed cabinet” (it even has storage drawers) it brakes the wall space and is excluded from the receptacle location requirement.
2. Forgetting my argument above and assuming that it should be included by code, there is no reference in the code as to the height of the receptacles. Therefore, there is no reason why the outlet couldn’t have been located above the bench as specified by the owner and me and still comply with the 6’ distance requirement. The height in itself wouldn’t make it non-compliant.
I welcome your comments.