Okay, in that case you were correct about the cabinet receptacle placement and have the needed receptacles for the wall space; however, you have just failed on working space for that cabinet.
IMO, a generator transfer switch would apply to the following:
110.26 Spaces About Electrical Equipment. Access and working space shall be provided and maintained about all electrical equipment to permit ready and safe operation and maintenance of such equipment.
(A) Working Space. Working space for equipment operat- ing at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of 110.26(A)(1), (A)(2), and (A)(3) or as required or permitted elsewhere in this Code.
Yeah.... The moment you asked the question I knew where you were going. And you're right...
Have to figure something here....