wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
(2014) 210.52(A)(1) says "Receptacles shall be installed such that no point measured horizontally along the floor line of any wall space is more than 1.8 m (6 ft) from a receptacle outlet." It does not say "from a receptacle outlet within that wall space."
So receptacles outlets outside of the wall space can be used to satisfy the 210.52(A)(1) requirement for a wall space. Thus if the fixed cabinet is, say, 6 feet wide, and the wall spaces on either side are only 3 feet wide, one centered receptacle on the outside of the fixed cabinet would be sufficient.
BTW, this strict reading also means that you can measure across doorways for the purposes of satisfying 210.52(A)(1). While I understand that common practice and the interests of safety preclude doing that, the text does not support such a prohibition. Unless there is further text I am missing, it sounds like a proposal for 2023 is in order.
Cheers, Wayne
So receptacles outlets outside of the wall space can be used to satisfy the 210.52(A)(1) requirement for a wall space. Thus if the fixed cabinet is, say, 6 feet wide, and the wall spaces on either side are only 3 feet wide, one centered receptacle on the outside of the fixed cabinet would be sufficient.
BTW, this strict reading also means that you can measure across doorways for the purposes of satisfying 210.52(A)(1). While I understand that common practice and the interests of safety preclude doing that, the text does not support such a prohibition. Unless there is further text I am missing, it sounds like a proposal for 2023 is in order.