- Illinois
- retired electrician
Look up the details ...not listed as required by 406.5(E). There is a lot of things that the manufacturers are doing like this. Note that the information that you posted only says that the receptacle itself is listed, and also note that its spill rating is based on IP 54 and not section 149 of UL 498 as required for the countertop listing. While is says it complies with UL 498, there are a lot of different products covered by that UL Projuse Standard. When you see "conforms to" in the manufacturer's information, that almost always means that they think they have designed and manufactured their product standard, but they have not actually had the product evaluated to that standard.Maybe I‘m reading the website wrong for the one I posted in #36?
From the site:
- Color: Stainless steel metal top
- Black outlet: 20 Amp GFCI
- Tamper resistant (TR) plugs
- Weather resistant (WR) outlet
- ETL listed for USA installations, # 4004534
- cETL listed for Canada installation, # 4004534
- CSA approved for Canada, #C22.2
- Conforms to UL 514A and 498
- UL listed receptacle, # E229322
- Water protection: IP 54 Spill proof rated
When I look up the ETL listing number, that device is listed as "cord reel or multioutlet assembly" and not as a countertop receptacle assembly.
) would not approve that!