That's exactly what I'm doing. No outltets added
210.12 requires the circuit conductors be protected not just the outlets, this is entirely different than GFCI requirements.
That's exactly what I'm doing. No outltets added
Even if you do not add outlets, if you install new branch circuit wiring supplying outlets 210.12 required AFCI protection of that new wiring. (IMO)
Bob, (IMO) the first sentence clearly states "outlets installed" as the trigger for the requirement .
Bob, (IMO) if you apply Charlie's rule to 210.12 the first sentence clearly states "outlets installed" as the trigger for the requirement of branch circuit arc fault protection. If the single word "installed" was not present your interpretation would be the correct one.
210.12 Arc-Fault Circuit-Interrupter Protection.
(A) Definition: Arc-Fault Circuit Interrupter (AFCI). A
device intended to provide protection from the effects of
arc faults by recognizing characteristics unique to arcing
and by functioning to de-energize the circuit when an arc
fault is detected.
(B) Dwelling Units. All 120-volt, single phase, 15- and
20-ampere branch circuits supplying outlets installed in
dwelling unit family rooms, dining rooms, living rooms,
parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, or similar rooms or areas shall be
protected by a listed arc-fault circuit interrupter,
combination-type, installed to provide protection of the
branch circuit.
Buck, the catcher on this is the term similar rooms. I can easily see a home theater room as a room an inspector is going to require AFCI. What we say here means squat, unfortunately, so I suggest calling the AHJ.
FWIW, The wine cellar IMO, would not require afci
Oh I thought we were talking code and not what you can get away with. You may get away with it but you may not also-- GC people are loaded why would you not use a AFCI- they certainly can afford it.It's Chatam at the GC. I might get away with it out there.
Where is the plug for the alarm?What about the Intercom System, its hard wired but I generally put the alarm on with it. And it plugs in.
Oh I thought we were talking code and not what you can get away with. You may get away with it but you may not also-- GC people are loaded why would you not use a AFCI- they certainly can afford it.
It's a bid job. They are exspensive. And I don't feel the need for them in a theatre.
Where is the plug for the alarm?
Where are you reading that?
As long as no new outlets are installed, you could use an approved junction box on the circuit and extend the branch circuit to the relocated or new panelboard without AFCI protection. There is no requirement that AFCI provisions be applied for a service change when no new outlets are installed.
Buck, I took the liberty to present this question to Ron Chilton, our state electrical inspector because I didn't buy Bob's thinking on it. :grin:
Here is his comment. It may not be spot on per NEC wording but that is the way he sees it.
Buck, I took the liberty to present this question to Ron Chilton, our state electrical inspector because I didn't buy Bob's thinking on it. :grin:
Here is his comment. It may not be spot on per NEC wording but that is the way he sees it.
Buck, I took the liberty to present this question to Ron Chilton, our state electrical inspector because I didn't buy Bob's thinking on it. :grin:
Here is his comment. It may not be spot on per NEC wording but that is the way he sees it.
Read it again. Use Charley's rule. Every word counts. You highlighted right up to the key word stopped.
How is this? (B) Dwelling Units. All 120-volt, single phase, 15- and
20-ampere branch circuits supplying outlets installed in
dwelling unit family rooms, dining rooms, living rooms,
parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, or similar rooms or areas shall be
protected by a listed arc-fault circuit interrupter,
combination-type, installed to provide protection of the
branch circuit.
We have also been down the road on the word installed and the verbage before. It means in the present tense, not ones at the initial installation. Like I said, if they remove that one word I highlited in red then your view would be the correct one. But as it stands, intentions or not, the code is clear on it. Installed...
Mike, yes all the words count and I was not trying to avoid the word installed.
So ...
I go to a house that is being remolded and because of that an existing home run supplying outlets must be re-routed and that requires adding a new section of NM to do that.
That new section of NM is a in fact branch circuit supplying outlets that are installed in a dwelling unit and that new section requires AFCI protection.
It appears you feel the word 'installed' means the act of providing a new outlet and IMO it is just talking about the location of being in a dwelling unit.
Read it again. Use Charley's rule. Every word counts. You highlighted right up to the key word stopped.
How is this? (B) Dwelling Units. All 120-volt, single phase, 15- and
20-ampere branch circuits supplying outlets installed in
dwelling unit family rooms, dining rooms, living rooms,
parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, or similar rooms or areas shall be
protected by a listed arc-fault circuit interrupter,
combination-type, installed to provide protection of the
branch circuit.
We have also been down the road on the word installed and the verbage before. It means in the present tense, not ones at the initial installation. Like I said, if they remove that one word I highlited in red then your view would be the correct one. But as it stands, intentions or not, the code is clear on it. Installed...