ericstac
Member
- Location
- Houston, TX
I have a 40 unit multifamily building that has drawings which show 3 phase service and single phase load centers. I have never seen this done like this before, is this even possible?
I have a 40 unit multifamily building that has drawings which show 3 phase service and single phase load centers. I have never seen this done like this before, is this even possible?
Yes, that is normal. With 40 units 13 will connect to phases A & B, 13 will connect to phases A & C, 13 more will connect to phases B & C with the remaining unit connecting to any two phases.
The house / landlord panel will likely be three phase.
Keep in mind this is. 208 volt so the reduced size wire allowances for dwelling units will not apply.
I take it this configuration is done primarily for cost purposes, or is there a rule against supplying 3ph to dwellings?
Where does the code say that?You can have 3-phase in a dwelling as long as it's not over 240v.....
Where does the code say that?
I was curious. I have never seen 480V at a house but I don't know that code prohibits it.Did I just make that up?
Maybe I'm thinking of 120v limitations to outlets in residential branch circuits?
Sent from my iPhone using Tapatalk
I think you will find limitations for luminaires, otherwise you just are not all that likely to need 277 or 480 volts in a dwelling.Did I just make that up?
Maybe I'm thinking of 120v limitations to outlets in residential branch circuits?
Sent from my iPhone using Tapatalk
Not common around here, and I have worked in a lot of rural homes, large and small. But we can generally get the POCO to put their transformer within a reasonable distance from the home.I visited a large rural property recently with step-up and step-down transformers to bring power more than 1000ft from the service to the dwelling. Granted, the higher voltage wasn't brought inside, but it could have been. I understand this sort of thing is fairly common.
Yes, that is normal. With 40 units 13 will connect to phases A & B, 13 will connect to phases A & C, 13 more will connect to phases B & C with the remaining unit connecting to any two phases.
The house / landlord panel will likely be three phase.
Keep in mind this is. 208 volt so the reduced size wire allowances for dwelling units will not apply.
we have never installed something like this before and not really understanding how you would connect the single phase meterstacks to the main, can you help with this?
So looking at everything to me it sounds like we install a 3 phase main, 3 phase meter stacks and then at the meter we switch to single phase when connecting the SER? and balance the load by how we connect the wires.
Does this sound right?