Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
Do they make it? It say EMT on the drawing but I thought it only came in RGS & PVC in that size. Thanks.
358.20 Size.
(A) Minimum. EMT smaller than metric designator 16 (trade size ?) shall not be used.
Exception: For enclosing the leads of motors as permitted in 430.245(B).
(B) Maximum. The maximum size of EMT shall be metric designator 103 (trade size 4).
O Lord, thank you for google. This way I don't ever have to go back in time and no journeyman can ever send me to go get something that doesn't exist or can't be used where I am. Thank you, Amen.
I'm scarred for life, I tell ya!
358.20 Size.
(A) Minimum. EMT smaller than metric designator 16 (trade size ?) shall not be used.
Exception: For enclosing the leads of motors as permitted in 430.245(B).
(B) Maximum. The maximum size of EMT shall be metric designator 103 (trade size 4).
O Lord, thank you for google. This way I don't ever have to go back in time and no journeyman can ever send me to go get something that doesn't exist or can't be used where I am. Thank you, Amen.
I'm scarred for life, I tell ya!
If it is not contain electrical conductors now or in the future would the NEC still apply? It shown as EMT on the electrical drawings.
If it is not contain electrical conductors now or in the future would the NEC still apply? It shown as EMT on the electrical drawings.
You might want to ask for clarification. If 6" EMT is shown on electrical drawings it is probably a mistake and you should probably find out what they really want.
Food service ... For the soda lines..... Def shown on the elec!!!
Food service ... For the soda lines..... Def shown on the elec!!!
Typically installed by the electrical contractor.
Food service ... For the soda lines..... Def shown on the elec!!!
And EMT I'm guess regardless of NEC?
If this is solely for beverage lines then the NEC does not apply. This new light weight stuff is better than the 6" RMC that we installed for beverage lines 20 years ago.![]()
What do you mean a "mother of a pull"? The 6" contains the soda line which we would not pull.Soda lines ... now, that changes EVERYTHING!
First off, I don't know of any light steel tubing in that size. EMT, by definition, does not exist beyond 4". This is a classic case of when you send out an RFI.
I'd avoid running anyof the pipe for the soda lines if you can. It's going to be a mother of a pull, and you don't want to take the fall for that. Let the GC or the soda guys do it.
Typically, 6" PVC (white) pipe is used. Take great care to have no more than TWO sweep elbows in the run, and lube the heck out of it. I'd use a larger pipe if I could.
What IS important is that you understand the electrical needs of the customer. The soda fountain will probably need at least four receptacles in the system. These are:
1- under the counter, to serve the compressor;
1- just above the counter, to serve the dispenser;
1- Up near the ceiling, to serve the ice maker they'll mount over the fountain; and,
1- back where the syrup is stacked, to serve the pump.
Even if they say 'no ice machine,' they'll probably mount an electric sign, so a receptacle up high is a good thing.