ramsy
Roger Ruhle dba NoFixNoPay
- Location
- LA basin, CA
- Occupation
- Service Electrician 2020 NEC
The code says no GFCI if >150v
That's right. What was I thinking?
The code says no GFCI if >150v
OP, what was your solution?
They are still exploring ways to get out of having to do this. ¯\_(ツ)_/¯
I’ll update when I have an answer.
Sent from my iPhone using Tapatalk
Refer to post 33.
What is that quote about the NEC? Something about... it says what it says, not what you think it says.
Good Luck.
There is a public input for the 2020 NEC that will clarify that it is the rating of the branch circuit that triggers the need for GFCI and not the rating of the receptacle.
Well dang, something makes no sense in the NEC and we’re supposed to follow it regardless. That’s a first.It is. But if I recall correctly the input was made by somebody from NEMA who stated basically that the current language made no sense and was possibly unenforceable as receptacles are not rated in "volts to ground".
:lol:Well dang, something makes no sense in the NEC and we’re supposed to follow it regardless. That’s a first.
I need to meet the requirements of 210.8(B)... GFCI in a commercial kitchen.
Equipment is a 60A 3-phase fryer.
Gear is Square D; QOB breakers only go up to 50A 3-phase GFCI, and they do not make molded case GFCI breakers.
Any ideas?
Sent from my iPhone using Tapatalk
amazingly, noWill we need to take loans on the 1st borns liftime income?
How much?amazingly, no
this is the best economical solution in the industry
Ouch, so $1360 time 9 for the OP