Are you sure about that?Not since the GFP was removed from SOME brands of AFCI.
Did you check it yourself?
Are you sure about that?Not since the GFP was removed from SOME brands of AFCI.
The only AFCI breakers that sill have GFP are Eaton CH, Siemens Non Plug On Neutral, Square D HOM and Square D QO.Are you sure about that?
Did you check it yourself?
The only AFCI breakers that sill have GFP are Eaton CH, Siemens Non Plug On Neutral, Square D HOM and Square D QO.
GE, Eaton BR and Siemens PON do not have GFP.
...
Manufacture info I have received over the years.This is based on ... ?
The only AFCI breakers that sill have GFP are Eaton CH, Siemens Non Plug On Neutral, Square D HOM and Square D QO.
GE, Eaton BR and Siemens PON do not have GFP.
That would be thoughts.Just a note to the OP that because they had the neutrals bypassed/capped/not running through the breakers, and they were working meant they had no ground fault protection component, otherwise they would have tripped instantly.
I don't think that's the case, because there were a couple of dual function arc/ground fault breakers bypassed in the same way. These aren't PON types; the breaker->neutral bar pigtail was also disconnected and capped offJust a note to the OP that because they had the neutrals bypassed/capped/not running through the breakers, and they were working meant they had no ground fault protection component, otherwise they would have tripped instantly.
Since when is any xFCI nuisance trip Completely false and not possible?You have stated many times that AFCI's will trip if you touch the ground and neutral at the same time with your hand. That is completely false and not possible.
I fixed it for me.That would be MY thoughts.
I never thought of defeating an AFCI in the manner they did. I feel inadequate.
Hmmm I wouldn't think that would work and would be seen as a ground fault immediately.... Maybe without the neutral connection the electronics that run the thing don't function?I don't think that's the case, because there were a couple of dual function arc/ground fault breakers bypassed in the same way. These aren't PON types; the breaker->neutral bar pigtail was also disconnected and capped off
That's my thinking. I've seen it done a few times; this is just the first time I've seen that used so systemically in one house. Most of the time it seems to be some hack handyman trying to get something to work instead of a professional electrician wiring a house. >:/Hmmm I wouldn't think that would work and would be seen as a ground fault immediately.... Maybe without the neutral connection the electronics that run the thing don't function?
Well this electrician wasn't professional either.That's my thinking. I've seen it done a few times; this is just the first time I've seen that used so systemically in one house. Most of the time it seems to be some hack handyman trying to get something to work instead of a professional electrician wiring a house. >:/
I could be convinced to go with gfpe instead of all AFCI and most of the new GFI requirements of the last several code cyclesIts too bad they removed the 30ma Residual Current Protection (RCD) from the AFCI spec, I found that to be the most accurate and beneficial function of an AFCI.
When I replaced my own panel at home (finally) last summer I installed some ground fault protection of equipment (GFPE) breakers so I could get that RCD 30ma protection feature, I figure if enough current is flowing on any of my equipment grounds to trip a 30ma I need to look into it.
If specs are open for requests then GFPE alarms with location data would be my choice.I figure if enough current is flowing on any of my equipment grounds to trip a 30ma I need to look into it.
Wi-Fi breakers, something else for China to hack.If specs are open for requests then GFPE alarms with location data would be my choice.
With xFCI costs an order of magnitude higher than thermal-magnetic devices, built-in CT's could ID Circuit number, and time domain reflectometry could plot location with length of home-run inputs, all with readily accessible WIFI data to eliminate control wiring.
Hold test button for 3 seconds to reboot firmware.Wi-Fi breakers, something else for China to hack.
The early versions of AFCI's all had a GFP component to them. I believe most if not all were 30mA GFP. They had to have it to meet listing standards at that time.What Wayne said.
To repeat and clarify, a breaker that is labeled only as AFCI and not GFCI *may* trip on a neutral-ground fault, but should not be *expected* to.
I don't think you will even trip a GFCI by doing that.I believe all types of AFCI trip by holding bare EGC & load Neutral in same hand, without touching each other.
This N-G resistance that trips all types of AFCI is considered a resistive fault, not to be confused with GFPE bolted N-G fault.