Tony S
Senior Member
- Location
- Resting under the Major Oak UK
My pockets aren’t deep enough to even consider buying it!
Isnt there also a none disclosure agreement? Or anyone can purchase it if they have enough?
Anyone can buy it. I don't think that there are any restrictions other than the standard copyright issues.
It's bizarre how some of you jump to conclusions and shoot right from the hip without a complete understanding of your target. You claim there are no series tests and yet most of you have never even read or researched the standard. You then find out there is indeed series tests, two in fact, and then you shift your focus onto the cable specimen conditioning process and plant your distrust flag there. But again, you have missed the mark.
Haven't researched the standard yet I was the one that brought up 15kv being used, something you left out. That and the fact if 120 volts doesn't trip the AFCI after 10 seconds 15kv is re-applied.
The point contact arcing test simulates the instantaneous-type arcing which occurs at 120V but at much higher fault currents (75A-500A) as a result of the simulated ground-fault. The carbonized arc tests are a real-world simulation for damaged, aging, misused, and other stress-related conditions over time. At 120V and as little as 200mA, even minor damage to a conductor may result in arcing which could break down the insulation and potentially create carbon buildup around the conductors. This is called the "build-up" or "conditioning" stage. As voltage is applied to the high resistance but conductive path, the carbon burns away resulting in more arcing and more carbonized deposits. Combustible gases are also created by this process.
I dont see many situations in the real world where insulation and cooper is turned into a superheated soup sealed up in tape. The energy released involving 15kv at 30ma across a fraction of a milli meter is just unreal.
From a series arcing standpoint unless someone is physically making and then breaking a clean cut conductor under load tens of thousands of times over and over I cant imagine that much incident energy ever being subjected to a wire in the real world.
This repetitive cycle ultimately sustains itself to a point where the chain reaction produces enough energy to ignite the combustible gases and surrounding combustible materials.
Where is the evidence that this is responsible for hundreds of thousands of home fires? It has never been proven this takes place behind walls or to what degree let alone how many cases have lead to fire.
So, how do you reproduce this real-world event in the laboratory? The solution derived after literally thousands of hours of research and testing is the "conditioning" process outlined in the standard today; carbonized fault simulators. The fault simulators reproduce, in a very short period of time, exactly what occurs on real-world branch circuits in weeks, months and years. A good analogy would be water frozen into ice. You can freeze water slowly or you can freeze water quickly. Both methods produce ice.
Physically break/make of a broken conductor or accelerated thermal aging might have been a better option reflecting the real world, but then again those might just giveaway what it really takes to get dangerous arcing without the assistance of high voltage.
Also keep in mind flash frozen water takes on a different structure then water frozen over a period of time.
The AFCI is not tested on the conditioning voltages, but at rated voltage (120V). The AFCI can't and doesn't know if the hazardous arcing is a result of simulated or natural conditioning.
There are still 2 issues:
1. 120 volts is applied immediately after 15kv has altered the insulation and copper. Analogy would be an HID lamp where a 4kv igniter strikes a low voltage high current arc with only an open circuit ballast voltage of only 100. The 4kv pulse is gone, but the arc can now be sustained at a far lower voltage.
2. I would imagine relays cycling between the transformer and 120 volts would produce transients seen by the AFCI.
Also, are those relays even rated to handle 15kv?
The "test" performed in the video linked above is absurd and most certainly doesn't simulate a "real-world" condition that could result in fire. In fact, it more closely resembles non-hazardous arcing that occurs in normally operating appliances, motors and switches which would result in unwanted tripping of the AFCI device. The gentlemen conducting the test apparently hasn't read the standard either nor understands the physics of hazardous arcing.
A loose connection at a terminal seems far more plausible to me than 15kv.
You have offered nothing about how AFCI breakers do anything of value in real life, only what they do in the lab.RJ & mbrooke, I love your enthusiasm. You both have incredible imaginations...
I have offered nothing but facts. You have offered nothing but baseless theories and innuendo. I have researched and studied every clause in the UL 1699 standard and currently serve as NEMA staff on the AFCI Task Force. You have never even read the standard and are basing your entire understanding of AFCI technology on ONE dissenting IEEE whitepaper and a YouTube video.
You have offered nothing about how AFCI breakers do anything of value in real life, only what they do in the lab.
We expect your response as posted Bryan, we also know we're being monitored ....~RJ~
RJ & mbrooke, I love your enthusiasm. You both have incredible imaginations...
I have offered nothing but facts. You have offered nothing but baseless theories and innuendo. I have researched and studied every clause in the UL 1699 standard and currently serve as NEMA staff on the AFCI Task Force. You have never even read the standard and are basing your entire understanding of AFCI technology on ONE dissenting IEEE whitepaper and a YouTube video.
I know I am never going to convince either of you to accept and support the previous work and actions of NEMA, UL, and CMP-2 with regard to AFCIs, but perhaps you will now be inclined to become more engaged and in-tune with the current and future developmental and regulatory activities that are and will be taking place with AFCI technology.
Work will be getting underway on the UL STP shortly as there are a few significant enhancements coming to AFCI devices in the very near future. It's an exciting time to be in our industry. I hope you and a few of the others here on this Forum are capable of keeping a more positive and open-mind as we keep moving forward.
Happy Independence Day!
Exactly. I was asked to explain how series arcing is tested in accordance with the standard. It's not my fault if you guys are asking the wrong questions or can't handle the correct answers. It's quite pathetic actually.
The problem with that for me is that you represent the industry, and I have a serious mistrust of any information from that source on the AFCI issue. That is because they lied to us from day one on this issue. The original proposals said that they had a device that would do what they now tell use a combination device will do...the only problem was that those original proposals predated the combination AFCI by about 13 years....
I have offered nothing but facts. ...
Happy Independence Day!
The problem with that for me is that you represent the industry, and I have a serious mistrust of any information from that source on the AFCI issue. That is because they lied to us from day one on this issue. The original proposals said that they had a device that would do what they now tell use a combination device will do...the only problem was that those original proposals predated the combination AFCI by about 13 years.
The industry has given me NO reason to believe anything they say about AFCIs.
As far as arcing and fires, there is little evidence that they cause many fires, but there is a huge amount of information that shows joule heating at poor connections do cause many fires, and even UL says that AFCI devices cannot detect joule heating (also known as a poor connection, a high resistance connection or a glowing connection).
So the wire sample is prepared as a parallel, not a series,
fault.
~RJ~
Again, your hanging your hat on the opinion and analysis of one person. The author is wrong. The arcing fault current is in series. This is the exact exhibit from the standard: (Follow the flow of current - it has but one path)
Don,
I would be so happy if anyone from NEMA or a manufacturer or the CMP could take quick look at the statistics involving fires and how AFCIs would change those numbers that you put together and at that point try find a compelling reason other than sales to require them.