Excellent video Mike --> https://www.youtube.com/watch?v=Da5SMuqQJ_8
However, that said, I have discovered a situation to which I interpret as a violation of 400.8, but to which I cannot find a reasonable alternative wiring method. I work at an industrial facility and we have centralized din-rail mounted UPS systems that come from the manufacturer with 15A receptacles to power external devices off of UPS power. Our plant has standardized on SJTOW cable for use with this application. The female end of the cord is cut and the wires are landed on terminals. Some of the remote panels require the flexible cable to be routed under the floor in existing raceway (cable tray, wireway, etc.) before terminating at a terminal strip in the remote panel for UPS supplied power. I spoke with several Electrical Engineer colleagues on the subject and I have engaged the UPS manufacturer and the manufacturer's representative on the issue as well, and everyone is in agreement that the above mentioned wiring method is the accepted wiring practice. However, according to your words in the video (link above), and according to the list of exclusions in 400.8, this wiring method appears to be a direct violation.
Is there an applicable exclusion to this that would allow this wiring method to be considered acceptable? If not, what would be the recommend practice of providing UPS power from a central din-rail mounted UPS systems with remotely powered devices/panels?
However, that said, I have discovered a situation to which I interpret as a violation of 400.8, but to which I cannot find a reasonable alternative wiring method. I work at an industrial facility and we have centralized din-rail mounted UPS systems that come from the manufacturer with 15A receptacles to power external devices off of UPS power. Our plant has standardized on SJTOW cable for use with this application. The female end of the cord is cut and the wires are landed on terminals. Some of the remote panels require the flexible cable to be routed under the floor in existing raceway (cable tray, wireway, etc.) before terminating at a terminal strip in the remote panel for UPS supplied power. I spoke with several Electrical Engineer colleagues on the subject and I have engaged the UPS manufacturer and the manufacturer's representative on the issue as well, and everyone is in agreement that the above mentioned wiring method is the accepted wiring practice. However, according to your words in the video (link above), and according to the list of exclusions in 400.8, this wiring method appears to be a direct violation.
Is there an applicable exclusion to this that would allow this wiring method to be considered acceptable? If not, what would be the recommend practice of providing UPS power from a central din-rail mounted UPS systems with remotely powered devices/panels?