Hi Everyone,
I have this huge problem with the simplest Air Conditioning inspection. The condensor has a name plate of 208 / 230. The inspector says it's a commercial single phase unit and needs me to change the unit to a better suited 240v condenser.
The service switch is a square D non-metallic breaker looking 60 amp rated switch that looks like a breaker. ( but it isn't ) He told me there is no amacity markings on it.
the unit has a max breaker data on it sasying not larger than 35 ampere ocpd. I installed wiring and ocpd for a 40amp , 35 is a rare breaker. 240.4b - I can go one size higher.
Is there a probllem with this. All inspectors in my area have no problem.
Can I get feed back?