- Lockport, IL
- Semi-Retired Electrical Engineer
Re: Big oops ... need suggestions
. . . . . Post #600!
600+ and right back at the beginingOriginally posted by charlie b:
Article 100:If the switch is part of the wiring system, then current is not taken from the system at that point.Outlet A point on the wiring system at which current is taken to supply utilization equipment.
Well, not really.Originally posted by marc deschenes:
600+ and right back at the beginning
Given the second sentence of the definition of Premises Wiring (System), I understand exactly the opposite.Originally posted by charlie b:
Do you understand that if the switch is part of the premises wiring system, then there is no outlet there, and no requirement for AFCI?
Especially in light of 404.14 that gets after the rating, as well as use, of a snap switch.Originally posted by al hildenbrand:
I can't get my head around how a "conductive material" that is inside a device that IS part of the wiring system IS NOT wiring.
I find that easy.</font>Originally posted by al hildenbrand: I can't get my head around how a "conductive material" that is inside a device that IS part of the wiring system IS NOT wiring.
The "conductive materials can be as substantial as you like, but they are not "wiring." Nothing in 404.14 changes that.Originally posted by al hildenbrand: Especially in light of 404.14 that gets after the rating, as well as use, of a snap switch.
These "conductive materials" are not insubstantial.
And there is absolutely no way that you can demonstrate in language of the NEC that the "conductive materials" inside a switch are included.Originally posted by al hildenbrand:Charlie B., there is absolutely no way that you can demonstrate in language of the NEC that the "conductive materials" inside a switch are excluded from the description of "That internal and external wiring".
The same can be said for all manner of wiring assemblies like cable, cord, receptacles, switchgear, the metal inside insulation that is known as "wire", busway.Originally posted by charlie b:
I find that easy.</font><font size="2" face="Verdana, Helvetica, sans-serif">
- <font size="2" face="Verdana, Helvetica, sans-serif">(1) If the switch is part of the wiring system, you don't have to look inside to see how it is constructed.</font>
So. I know you are not taking a leap of illogic with this one.Originally posted by charlie b:
- <font size="2" face="Verdana, Helvetica, sans-serif">(2) The definition of premises wiring system includes things that are certainly not "wiring." It includes hardware and fittings, neither of which is "wiring."</font>
What does "wiring" always look like that you can draw this exclusion?Originally posted by charlie b:
- <font size="2" face="Verdana, Helvetica, sans-serif">(3) The "conductive material" inside the "no-frills switch" does not look like wire, and it doesn't do a wire's job.</font>
Wiring goes from one point to another point.Originally posted by charlie b:
- <font size="2" face="Verdana, Helvetica, sans-serif">I once said that I would lump Busway with "wiring," even though it doesn't look like wire, for lack of a better category. But it does do the same job as wire, and it is part of the premises wiring system.</font>
You and I are conductive materials. Does that make us "wiring"?Originally posted by al hildenbrand:But there is no language that expresses the distinction between conductive material and wiring.
That proves my stance. If the NEC doesn't prohibit it, it is.Originally posted by charlie b:
It is easily distinguishable. Upon movement of the switch handle, the conductive materials will either mate, and complete a connection with each other, or separate, and open the connection with each other. A wire never is used for such a purpose.Originally posted by al hildenbrand: A switch has two points on it that are connected together by the "conductive materials" inside the switch. This is indistinguishable for the "behaviour" of wiring.
Come on, you can do better than that. This isn't about what is "prohibited," and what is not. It is about what is an "outlet," by the NEC's definition, and what is not.Originally posted by al hildenbrand: That proves my stance. If the NEC doesn't prohibit it, it is.
And I would say the same for them. Each item on that list is part of the premises wiring system, and I don't have to tear them apart to see if anything inside them would change that fact. Besides, if I did tear some of them apart to look inside, I might void their UL listing.Originally posted by al hildenbrand:The same can be said for all manner of wiring assemblies like cable, cord, receptacles, switchgear, the metal inside insulation that is known as "wire", busway.Originally posted by charlie b: