kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
They chose to place the test current resistor from neutral to one phase so that they could use the same button and resistor value that they use for the single pole units. There is no reason they could not have used a resistor with twice the ohm value and twice the power rating and connected it between L1 and L2. But they did what they did. So it is a manufacturers' decision rather than a physical law that requires the neutral pigtail connection.
And of course if there is a current carrying neutral to the load, it must pass through the current coil in the GFCI. That part is a physical law.
I cannot find any fault in your use of "typically" since it is hard to get more typical than SquareD.
Besides the "test feature" not working the remaining question is whether or not everything else still works with no neutral. I really have no clue, I guess it would depend on how the control circuitry works. Next question is does it still work if one of the ungrounded conductors is open ahead of the device?