I'm still not convinced that the water lines should be tied to the neutral/ground wire system at the service.
Well you are mistaken, besides it being required by code it is safer to bond the water lines then not.
I'm still not convinced that the water lines should be tied to the neutral/ground wire system at the service.
And I would think that this is extremely rare .... not even convinced it happened they way you said it did.I appreciate all the opinions. However after what happened in my case, I'm still not convinced that the water lines should be tied to the neutral/ground wire system at the service. I would think this has happened many times and most EC's wouldn't know about most cases since it would be a utility problem not an EC problem to correct. It would be nice if Mike Holt chimed in on this one.
And I would think that this is extremely rare .... not even convinced it happened they way you said it did.
How do you know the neutral was energized?
Did you measure voltage at the time and if so between what points.
Exactly what type of damage did you have?
I have no doubt that you can have damage that would result in a grounded to ungrounded fault on the service drop....I have extreme doubts that the fault energized the neutral....your description is exactly what happens when the service neutral opens.So which would you think has a better chance of happening; 1) My case, which was the service drop hot wire insulation deteriorated or was rubbed off by a tree branch causing it to contact the bare neutral/ground wire that it was wrapped around thus energizing all my neutral and ground conductors in my house as well as my water line that the service ground is tied too or 2) A circuit in my house decided to disconnect itself from a device or outlet and craw under the house and touch my copper pipes under the slab? Note: my water heater is piped with CPVC.
I didn't want to write a book on what happened but seems I need too since some don't get it; I was in my house and all of a sudden I heard a lot of popping and smelt and saw smoke coming from some surge protectors, I immediately went out side and tripped my main 200 amp breaker. I checked voltage coming in and found I had 220v between line side neutral and one hot leg and 220v between both hot line legs. I checked the service drop wire myself and found what happened, which is what I've posted many times in this thread. Just in case you think I'm an idiot, the power company confirmed it and cut out the section and replaced it. The voltage on my neutral damaged a lot of appliances and TV's, etc.
I'm not hear to convince people what happened, I'm certain of what happened. I just wanted some opinions on whether its safer not to tie the water pipe to the ground from the service since in my case it could have killed someone if they were taking a shower or washing hands, etc. I think theres a great chance and probably very common for number 1 above to occur and no chance of number 2 occurring.
Really unwise installation. Either by the electrician or the POCO tech who made the connection.
Had the same thing happen 3 weeks ago. #10 out of the weather head was drapped over the #2 triplex messenger, it welded on to the neutral, 240 neutral to B phase. It burned up a gate controller that caught fire, along with surge arrestors. A QO2 panel lug pretty much melted off the plastic. All this was fed from a 1ph 25kva pole mount xfrm 12kv pri 120/240 1700ft away, never blew the cutouts.
(Trying to figure image uploads)
Had the same thing happen 3 weeks ago. #10 out of the weather head was drapped over the #2 triplex messenger, it welded on to the neutral, 240 neutral to B phase. It burned up a gate controller that caught fire, along with surge arrestors. A QO2 panel lug pretty much melted off the plastic. All this was fed from a 1ph 25kva pole mount xfrm 12kv pri 120/240 1700ft away, never blew the cutouts.
(Trying to figure image uploads)
If an ungrounded conductor comes in contact with the neutral (bare) conductor from a service drop and your properly grounded per NEC at the service to ground rods and water pipe, its 100% that your copper water pipes will be energized.
Exactly same thing that happened to me, except in my case it was the main service conductors from the service drop, which were probably #1 AL. If an ungrounded conductor comes in contact with the neutral (bare) conductor from a service drop and your properly grounded per NEC at the service to ground rods and water pipe, its 100% that your copper water pipes will be energized.
The utility primary fuses are not sized to protect the transformer or the transformer secondary conductors. They are only sized to prevent a fault on the load side of the cutout from taking out the distribution circuit.Not enough incident energy to blow cutouts? More then likely not sized correctly. I was curious at what length in wire would it have to be to just look like a load?
Only if the neutral was open in the first place.If an ungrounded conductor comes in contact with the neutral (bare) conductor from a service drop and your properly grounded per NEC at the service to ground rods and water pipe, its 100% that your copper water pipes will be energized.
Only if the neutral was open in the first place.
Roger
Correct, but that will not increase the line to neutral nor the line to line voltages, in fact, both of those voltages will be below normal.. In addition, everything connected to the electrical grounding system will be at this elevated voltage. In the case of a fault on the line side of the service OCPD, normally the fault burns clear, but that could take some time.If the neutral was neither open nor compromised, then until an OCPD intervenes the water pipe could be energized to as much as half of the line to ground voltage of the faulted wire. More if a reduced size service neutral was used. It will not be raised to the full open circuit line potential.
The condition will normally not last very long though.
It seems to me that if L1 shorts to N, moving N and EGC in the direction of the L1 voltage, it would necessarily raise the L2 to N voltage.Correct, but that will not increase the line to neutral nor the line to line voltages, in fact, both of those voltages will be below normal.. In addition, everything connected to the electrical grounding system will be at this elevated voltage. In the case of a fault on the line side of the service OCPD, normally the fault burns clear, but that could take some time.