No - such thoughts simply lead to drinking. I'm going to get a tattoo that says, "The existing language has been used successfully for years."
I'm pretty sure I could dig up a CMP response to counter that argument.
Well ,. sounds like you'll have the shovel out,. so , by all means start digging.
But if it is one of these ,don't bother
5-235 Log #1834 NEC-P05 Final Action: Reject
(250.104(A)(1))
__________________________________________________ __________
Submitter: Mark T. Rochon, Mark J. Rochon Master Electrician
Recommendation: Revise as follows:
General Combination metal water piping system(s) separated by nonmetallic
water piping system(s) where may become energized installed in or attached to
a building or structure shall be bonded to the service equipment enclosure, the
grounded conductor at the service, the grounding electrode conductor where of
sufficient size, or the one or more grounding electrodes used.
Substantiation: Nonmetallic water piping systems are being inserted between
our metal water piping system and today?s code is not recognizing these
changes.
Panel Meeting Action: Reject
Panel Statement: The conditions indicated in the substantiation are already
covered by 250.104(B) where there is not a complete metallic water piping
system.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15
__________________________________________________ __________
5-236 Log #2432 NEC-P05 Final Action: Reject
(250.104(A)(1))
__________________________________________________ __________
Submitter: Robert P. McGann, City of Cambridge
Recommendation: Revise text to read as follows:
Metal water piping system(s) that is likely to be energized , installed in or
attached to a building or structure shall be bonded.
Substantiation: With much expanded use of plastic water piping system(s)
isolating section of metal piping systems. This type of installation leaves
contractors and inspectors what is required to be bonded.
Panel Meeting Action: Reject
Panel Statement: The requirements of 250.104(A) apply to complete metallic
water piping systems. Where there is no complete metallic water piping
system, then the requirements of 250.104(B) would apply for those portions of
isolated metal water piping system likely to become energized.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15
__________________________________